Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Adding routers and moving devices in an existing LonMaker installation.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Adding routers and moving devices in an existing LonMaker installation.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
944 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Adding routers and moving devices in an existing LonMaker installation.

Picard Product_Support
‎2018-09-10 03:15 AM

Issue

 Routers and Channels must be added in the proper order to successfully move devices.

Environment

  • LonMaker
  • Vista
  • TP/FT10

Cause

LonMaker will only allow devices to be moved to a location on the network that has an established communications path to the Network Interface. Attempting to do so will result in LonMaker denying the request to move the device. 

Resolution

This example consists of a network containing L-IP Ethernet to TP/FT-10 Router (LIP) with a single TP/FT-10 Channel (FT10) and six devices. (Device 1-6). The topology and hardware used in a LonMaker network can vary greatly but the same technique should be followed to successfully insert routers, channels, and move devices around in the network.
  

  1. 2 TP/FT-10 to TP/FT-10 routers (LPR10_1-2) will be placed on the existing TP/FT-10 Channel
  2. Drag the Channel Stencil onto the drawing and designate it as a TP/FT-10 Channel.
  3. Drag the appropriate Router Stencil into the drawing.
  4. The New Router Wizard will then allow you to name the Router (LPR10_1)and designate the Near/Far side Channels. Channel A (near side) is designated on the old FT10 channel and LPR1 Channel B (far side) is designated on the new FT10_1 Channel.


     
  5. Repeat steps 1 through 4 for LPR2. which will result in the following

  6. The original TP/FT-10 Channel can now be renamed to represent the FT10 Backbone.
  7. Select devices to be moved onto the new FT10_ 1 and FT10_2 channels.
  8. Right Click each device and select "Move Device > Change Channel".  (Device1)
  9. In the Channel Select Wizard, Change the Destination Channel to the Desired new Channel. (FT10_1)


  10. Repeat for Devices 2-5 on the FT Backbone to the desired new FT-10 Channel.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6312
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of