Adding an event to a Xenta Time Schedule results in "The maximum number of total events is exceeded."

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Adding an event to a Xenta Time Schedule results in "The maximum number of total events is exceeded."
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1616 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Adding an event to a Xenta Time Schedule results in "The maximum number of total events is exceeded."

Picard Product_Support
‎2018-09-10 02:23 AM

Issue

Not allowed to add a new event to a Xenta Time Schedule through Vista Workstation. One of the following errors results:

The maximum number of total events is exceeded.

 

The maximum number of week events is exceeded.
Only alternative events can be added.

 

The maximum number of alternative events is exceeded.
Only week events can be added.

Environment

  • Vista Workstation
  • Xenta Time Schedules
  • Xenta programmable controllers
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
  • Menta

Cause

The adjustable setting for the maximum amount of events allowed in a single Time Schedule object has been exceeded.

Resolution

  1. Verify how many weekly and how many alternative events are allowed. This is available on the time schedule editing dialog in the lower right hand corner.
  2. Click the "All Events" button to display all previously defined events.
    • Weekly events are displayed with a dash "-" in the From Date, To Date columns
    • Alternative events will have a date in the From Date, To Date columns. The year may or may not be **** if this is a yearly recurring event.


       
  3. Count how many weekly and how many alternative events are defined. If possible, delete unneeded events to clear space for new events. If a holiday is not set to occur yearly, then old events from years past may still be defined and can be deleted.
  4. If all of the events are required, then the capacity for the time schedule must be increased in Menta.
    • Edit the Menta file
    • Double click the TSCH block
    • Increase the max for Week Charts, Holiday Charts, or both as needed.


       
  5. Download the Menta changes to the controller and more events can be added.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5968
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore