Issue
Add Xenta trend log is grayed out when right clicking on point in a programmable Xenta controller and selecting Create Trend Log.
Environment
- Xenta Programmable Controller
- Menta
Cause
There are no available trend logs in the Menta application. There have to be empty trend logs in Menta for this to work.
Resolution
- Edit the file In Menta
- Go to Options > Trend Logs
- Click on the 'up arrow' to increase the number of available trend logs.
- Save the application to the Vista Database
- Download to the controller.