Access denied error when editing the Continuum menu or the x86 path is incorrect

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access denied error when editing the Continuum menu or the x86 path is incorrect
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1825 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access denied error when editing the Continuum menu or the x86 path is incorrect

Picard Product_Support
‎2018-09-07 08:46 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:11 PM

Issue

The user logged into Windows doesn't have permissions to the folder that contains the Continuum.mnu file,  the file is set to read only or the path in the continuum.mnu is incorrect.

Product Line

Andover Continuum

Environment

  • Continuum
  • Windows XP
  • Windows Vista
  • Windows 7
  • Windows Server 2003
  • Windows Server 2008

Cause

Permissions are restricted to the Continuum.mnu file or the path in it is incorrect.

Resolution

One of the follow solutions will resolve this:

  1. Click to download an edited default path Continuum.mnu and Menu.bmp  (links for the default path C:\Program Files (x86)\Continuum)
    Copy these files to each workstation that has an incorrect path
  2. Manually edit the file yourself if you have a path that is other than (C:\Program Files (x86)\Continuum)
    1. Grant permissions to the folder.
      The folder that contains the Continuum.mnu can be located by editing the Cyberstation in Continuum Explorer.
      WS Edit> Preferences tab> The file name of the main menu  Ex. c:\program files\continuum\userprofile\continuum.mnu
    2. Right click on Continuum.mnu and select properties. Deselect Read Only if it is selected.
    3. Change the path to the Continuum.mnu file to a folder that you have access to and copy the continuum.mnu to it.
      Ex. c:\program files\continuum\continuum.mnu
    4. While in edit mode, right click on each of the buttons and select Properties
      Use the browse button to select the correct x86 path (C:\Program Files (x86)\Continuum)

Repeat this for each of the buttons and then save the Continuum.mnu file

Copy these files to each workstation that has an incorrect path

Also see Continuum.mnu file with C:\program files (x86) on 64 bit PCs points to C:\program Files and shows a ....

Labels (1)
Labels:
  • Andover Continuum
Attachments
Continuumx86MNU.zip
Tags (2)
  • Find more articles tagged with:
  • 4873
  • screen
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of