Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Access Expert supervised inputs EOL resistor configuration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert supervised inputs EOL resistor configuration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
3516 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert supervised inputs EOL resistor configuration

AbeMeran Mentor
‎2021-11-04 11:57 AM

Last Updated: ContentModerator Explorer ‎2025-09-01 03:34 AM

Issue

Proper configuration of supervised inputs, Mercury IO modules (i.e MR52) versus Continuum IO modules (AC1/AC1Plus) for transitioned Continuum sites.

Product Line

EcoStruxure Access Expert

Environment

  • Access Expert Controller
  • Access Expert Reader Interface
  • Access Expert Premise Software
  • Access Expert Hosted Software
  • Continuum AC-1 IO Module

Warning

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Cause

Guidance is needed on the proper configuration of Access Expert custom EOL resistor tables in order to achieve full supervision of inputs associated with readers/doors.

Full supervision in this context means not only being able to detect normal input operation (activation/deactivation) but also detection of attempts to tamper with the input's circuit (short circuit, open circuit, grounding, the introduction of foreign voltages, etc.)

Please note that not all resistor configurations can detect all the various circuit issues, for example, a NO Series resistor configuration can't detect a cut in the wire given that the open circuit is the normal state for the Deactivated value of the input.

The resistor configuration that provides the most supervision is the Series/Parallel configuration, using 2 resistors is possible to detect both short and open circuits.

Resolution

Continuum supported a fixed 10K Ohms resistance for supervised inputs, furthermore, Continuum IO modules (AC1/AC1Plus) transitioned to Access Expert under an AX-SSC controller continue to operate with Continuum firmware, this means that they do not support the custom EOL tables in Access Expert, the only configuration that is possible for AC1/AC1Plus modules is the mode of connection of the resistor (parallel, series or both).

 

Also, when using 2 resistor configuration, the placement of the resistor is different in Continuum compared to Mercury hardware

 

CONTINUUM

ContinuumTwoResistors.PNG

When the switch is open only the resistor on the left is seen by the input.

When the switch is closed, the two resistors are presented to the input in parallel with each other resulting in the input reading half the sum of the total resistance value.

 

SECURITY EXPERT

 

Mercury (2).PNG

 

 

When the switch is open, the two resistors will be presented to the input in series with each other resulting in the input reading the sum of the two resistors value. 

When the switch is closed only one resistor is presented to the input

 

For the above reasons, Continuum transitions sites where the AC1/AC1Plus has been replaced with Mercury hardware like the MR52 for example, need to configure one or more custom EOL table(s) for 10K resistors.

 

*** The sample tables provided below contain resistance values calculated to take into account wide variations in total supervised loop resistance due to wire distance, gauge etc., supervised loops should be installed in accordance to distance and gauge guidelines for wires as well as recommended resistor tolerance.

It may be necessary to make adjustments to the resistance values in the tables on a site by site basis.

 

See below sample tables for all six possible 10K resistor configurations

 

  1. Normally Open Parallel (10K-NO-P)
  2. Normally Closed Parallel (10K-NC-P)
  3. Normally Open Series (10K-NO-S)
  4. Normally Closed Series (10K-NC-S)
  5. Normally Open Series/Parallel (10K-NO-SP)
  6. Normally Closed Series/Parallel (10K-NC-SP)+

1. Normally Open Parallel (10K-NO-P)

NO-P.PNG

2. Normally Closed Parallel (10K-NC-P)

NC-P.PNG

3. Normally Open Series (10K-NO-S)

NO-S.PNG

4. Normally Closed Series (10K-NC-S)

NC-S.PNG

5. Normally Open Series/Parallel (10K-NO-SP)

NO-SP.PNG

6. Normally Closed Series/Parallel (10K-NC-SP)+

NC-SP.PNG

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (5)
  • Find more articles tagged with:
  • AbeMeran21
  • AbeMeran22
  • eol
  • inputs
  • resistor
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore