Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

AS controllers dropping offline (BACnet Command Priority related).

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • AS controllers dropping offline (BACnet Command Priority related).
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2141 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

AS controllers dropping offline (BACnet Command Priority related).

Picard Product_Support
‎2018-09-06 09:26 AM

Issue

Following an upgrade to V1.5 from V1.4 the AS goes off/ online.

Environment

Automation Server AS

Enterprise Server ES

V1.50 and above.

Cause

Following an upgrade to V1.5 from V1.4 the AS goes off/ online caused by an incorrect setting of the Default Priority Level.

Resolution

This issue only occurs if the site has changed the BACnet "Default Priority Level" from the default value of 16, to 8 or a smaller numeric value in the Automation Server while running in V1.4.

So before upgrading to 1.5 make sure the "Default Priority Level" within the Automation Server is set to 9 or higher.

If the system has been upgraded with the incorrect values, then: 

  • If the site uses single servers, or the ES/AS communication still operates correctly, then this can be corrected by changing the setting in both the AS and the ES to a value of 9 or higher.
  • If after upgrading a multiserver configuration and the AS does not stay online, then a Hotfix can be used fix the problem using the following steps:

1. Apply the hot fix #1.5.0.4301; available from Product Support Services

2. Fix the multi-server (by detaching/re-attaching the servers)

3. Correct the two properties (AS and ES).

WARNING: It is essential for any BACnet system at 1.5 or later that the "Default Priority Level" has a larger numeric value than the "Force Priority Level, otherwise some BACnet functions may not behave as expected, this also applies even if the hot fix is installed.

The effects of not setting the Default above the Force Priority level are:

1. If Force Priority Level is equal to the Default Priority Level:

Changing the Value of a BACnet value or a BACnet output object will cause the Value to appear Forced. This applies to the BACnet objects in both SBO servers and those in 3rd party BACnet devices.

2. If Force Priority Level has a larger numeric value than the Default Priority Level:

Changing the Value of objects mentioned above will cause the Priority Override icon overlay to be turned on next to the Value property in the WorkStation’s property grid.

Note: The Default and Force Priority Level are located/ defined in the Green "System" folder, "Interface Manager", "BACnet" for each Server.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 16844
  • issued
  • tpa-sbo-14-0005.00
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore