AMT message "Time-sync failed"
  • AMT message "Time-sync failed"
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 01:15 PM
I/NET Seven
AMT
The Time-sync failed message indicates that an attempt to sync time with a DCU has failed.
Time synchronization is a function of DCU Synchronization. This is only intended for use with direct-connect, TCP/IP or AD/AA communication. If your site is using Integrated Dial or NPR Dial connection, this explains the alarm and must be deactivated.
To View the systems DCU synchronization settings.
  1. Log into I/NET and select Edit>Host Computer>Network functions.
  2. From there you can select a link via a dropdown menu
  3. view the "Sync" setting for each controller.
  4. If Sync is enable on any controller that are offline or no longer exist, disable synchronization (and any other Host function)
  5.  If time sync is not desired, it can be disable which will also remove the alarm.
  6. If time DCU synchronization is desired, This is likely an indication of a communication failure. Determine if this has occurred on an entire Controller LAN or just a single controller. Use this as a starting point and work towards the PC looking for communication errors.
  • TAC INET
  • 6246