AMT is Displaying Link 200 and a partial point address.
  • AMT is Displaying Link 200 and a partial point address.
‎2018-09-07 01:39 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:32 AM
I/NET site
Error Message AMT is Displaying Link 200 and a partial point address
AMT can report a LINK 200 + a partial point address. When this occurs the system has defaulted to an error handling code to let the system programmer know that there is a hardware addressing conflict in a direct connect system.
To correct this; open active profile in the I/NET configuration editor and modify the link configuration editor.
The error generally occurs when the host hardware address is different then the actual hardware address.
For example: 7801 Tap is addressed "0" and the Host hardware address is something other than "0". When connecting to a Host/Link/Lan tap (either a 78010 that connect directly to the controller lan or an emulated 78010 on a controller), the hardware address is always 0 and cannot be any different.
Please read TAP and Repeater TCON 101 for a more detailed explanation on configuration parameters.
  • TAC INET
  • 1999