ADI FSCO Panel Integration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • ADI FSCO Panel Integration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1486 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

ADI FSCO Panel Integration

Picard Product_Support
‎2018-09-07 02:10 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-03 06:28 AM

Issue

ADI FSCO Panel Integration

Product Line

TAC Vista

Environment

  • ADI FSCO Panel
  • Xenta 913

Cause

Integration to an ADI Fire/Smoke Control Panel.

Resolution

This document details the process for integrating an ADI FSCO Panel (www.adipanel.com) with a TAC Xenta 913 through the ModBus serial interface.

Comm Settings

In XBuilder, right click the "RS232-485 A" Serial Port, add a ModBus Slave interface. The comm settings necessary are shown below:

commsettings.png

 

The ADI FSCO Panels speak RS232. The 913's baud rate is adjustable in XBuilder from 300 to 19200. The panel's baud rate is adjustable via DIP switches from 2400 to 19200. There is no right or wrong speed, they just need to match. Parity is even, 7 data bits, 1 stop bit, and ASCII framing mode.

On the ModBus serial line slave, right click and add a device. If it has not been created yet, you will need to create a device template first. The device requires a ModBus address. With an ADI FSCO Panel, this address is always 1.

Physical Connections

The RS232 port is an RJ45 port on the left front of the 913 labeled “A.” If you are creating your own patch cable to tie into the ADI FSCO Panel, the pin-out is as follows:
 

1 - White Orange
2 - Orange
3 - White Green – TXD
4 - Blue – RXD
5 - White Blue – GROUND
6 - Green
7 - White Brown
8 - Brown

 

colorcodes.png

 

TXD ties to the ADI FSCO Panel on the terminal block labeled "IN." RXD ties to "OUT" and GROUND ties to "GND."

Signal Connections

When populating connection objects between an ADI FSCO Panel and a Vista database, the best option is to use a Multi-Connection Object. Right click on the root folder in the System pane of XBuilder and select New > Object > Multi-Connection Object. The Multi-Connection Object can be populated by dragging and dropping points from the ADI Device Template and Menta.

The Send Option in the Connection Manager lets you select either Periodically, Write on change, or Write initially and on change. Choose to write initially and on change. Each point also has a designated Period. Just because a point is not set to update periodically does not mean the period ceases to have any effect. If too many points are on the same period, it can overwhelm the 913. So regardless of the Send Option, the Period (s) should be staggered. Set the first 20 points to 10 seconds, the next 20 points to 11 seconds (for example – in reality, just avoid having hundreds of points at the same period.)

When finished populating all data fields of the Connection Manager, hit the Validate button on the bottom left corner and make sure there are no errors.

Menta Programming

Menta files that accept data from an ADI FSCO Panel do so through PVBs and PVRs. These come default with the "Backup" option selected. This is used to store the value in non-volatile memory on power loss. When using a PVR for a setpoint, this is a good thing. However, when something is constantly writing a value to this public variable, and it in turn is constantly writing values to flash memory, it can cause the controller to lock up and stop working. You must de-select the "Backup" option from any PVBs or PVRs in a Menta file that are accepting data from a connection object in a 913.

Disclaimer

This document is intended to address some of the most common (and most commonly overlooked) settings when integrating with an ADI FSCO Panel through a serial ModBus connection. Contact ADI for product information and to ensure that the correct FSCO Panel is ordered to facilitate this type of integration. No guarantee can be made that changes to the physical configuration, communication settings, or software format have not been made, so always check with your ADI sales representative first.

Labels (1)
Labels:
  • TAC Vista
Tags (4)
  • Find more articles tagged with:
  • 3620
  • fireman
  • firemen
  • override
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of