ACX7xx swipe of unknown card results in reader LED blinking slowly
  • ACX7xx swipe of unknown card results in reader LED blinking slowly
  • AbeMeran
    AbeMeran
‎2018-09-06 10:19 AM
ACX7xx (ACX701, ACX781) swipe of card that is not in DB results in reader LED blinking slowly for over a minute.
Then an access events 'No response from access server' is logged in the access event log.
Andover Continuum
  • CyberStation
  • ACX701
  • ACX781
AccessServer system variable set to an incorrect value. For example, a value of 1 will cause the ACX to attempt a remote validation to the controller with ACCNetId of 1, whether it exists or not.
  1. Set the AccessServer to 0 (zero) if not remote validation is desired, or set it to the ID of the Primary Access Server workstation.
  2. NOTE: The old ACXs require a reset when the value of AccessServer is changed.
  3. After making the changes reload the controller.
  • 13526
100% helpful (1/1)