A station will not start in an I/A Series R2 (Niagara) UNC; errors similar to: "Invalid jar: /tffs/modules/coreRuntime-2.301.522.v2.jar, WARNING: Module alm 2.301.522.v1 [/t...

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • A station will not start in an I/A Series R2 (Niagara) UNC; errors similar to: "Invalid jar: /tffs/modules/coreRuntime-2.301....
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1289 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

A station will not start in an I/A Series R2 (Niagara) UNC; errors similar to: "Invalid jar: /tffs/modules/coreRuntime-2.301.522.v2.jar, WARNING: Module alm 2.301.522.v1 [/t...

Picard Product_Support
‎2018-09-06 01:09 PM

Issue

A station will not start in an I/A Series R2 (Niagara) UNC; errors similar to:

"Invalid jar: /tffs/modules/coreRuntime-2.301.522.v2.jar
WARNING: Module alm 2.301.522.v1 [/tffs/modules/alm-2.301.522.v1.jar]
  Missing dependency: coreRuntime-2.301
WARNING: Module lib 2.301.522.v1 [/tffs/modules/lib-2.301.522.v1.jar]
  Missing dependency: coreRuntime-2.301
WARNING: Module lonSiebe 2.301.522.v1 [/tffs/modules/lonSiebe-2.301.522.v1.jar]
  Missing dependency: coreRuntime-2.301
WARNING: Module lonworks 2.301.522.v1 [/tffs/modules/lonworks-2.301.522.v1.jar]
  Missing dependency: coreRuntime-2.301
WARNING: Module ndio 2.304.522.v1 [/tffs/modules/ndio-2.304.522.v1.jar]
  Missing dependency: coreRuntime-2.301
WARNING: Module programLib 2.301.522.v1 [/tffs/modules/programLib-2.301.522.v1.jar]
  Missing dependency: coreRuntime-2.301
WARNING: Module vlon 2.301.522.v1 [/tffs/modules/vlon-2.301.522.v1.jar]
  Missing dependency: coreRuntime-2.301
WARNING: Module vlon 2.301.522.v1 [/tffs/modules/vlon-2.301.522.v1.jar]
  Missing dependency: lonworks-2.301
WARNING: Module webUser 2.301.522.v1 [/tffs/modules/webUser-2.301.522.v1.jar]
  Missing dependency: coreRuntime-2.301
FATAL: Could not load class "tridium.tools.StationMain".

Environment

I/A Series R2 UNC, all builds

Cause

The cause of this error is not known.

Resolution

  1. Do a full install (upgrade) including upgrading the OS, NRE and niagarad.


  2. On the configure modules screen,  check the "Upgrade/Add" for all modules shown as installed (this forces the module to be reloaded).
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6572
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of