Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

A new InVue Client computer displays "Access is denied" for each OCX on a graphic display. How can this be corrected?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • A new InVue Client computer displays "Access is denied" for each OCX on a graphic display. How can this be corrected?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1984 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

A new InVue Client computer displays "Access is denied" for each OCX on a graphic display. How can this be corrected?

Picard Product_Support
‎2018-09-11 06:30 AM

Issue

A new computer has been configured as an InVue Client computer.  In Viewer, when displaying a typical graphic screen, the dynamic values for each OCX is replaced with the words "Access is Denied".

What causes this message and how can it be corrected?

Environment

InVue

Wonderware for Intelligent Buildings (WIB)

Cause

Primarily a Windows permissions issue or incomplete communications setup.

Resolution

Try each of the following to correct the problem:

Make sure DCOM is enabled (Start -> Run -> dcomcnfg) and running on both the client and server computers.
Use "telnet" command to see if port 135 is open and available for DCOM.
Use dcomcnfg.exe to modify its settings:

  • On Default Properties tab, verify that "Enable Distributed COM" is checked, default authentication level is "Connect" and Default impersonation level is "Identify"
  • On Default Security tab, Default Launch Permissions - click Edit ... button, verify that the Administrators group is shown and has "Allow Launch" permission"
  • On Default Security tab, Default Configuration Permissions - click Edit ... button, verify that the Administrators group is shown and has "Full Control" permission"

Windows login account for the client pc must exist on the server as well -- same username and password -- administrative privileges mandatory
Ensure wwuser.exe (factorysuite/common folder) reflects the local computer name and administrative user account

Re-do the DDE Shares as outlined in Tech Bulletin 02-26 on the client computer.

Turn off any firewall and disable/remove anti-virus / anti-spam program or service.

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • 15395
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore