Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

A known cause of communication problems with GCM Ethernet NIMs (GCM-ETH-001) is entering incomplete IP addresses in the NIM block. The NIM block requires full octets (3 digits) in ...

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • A known cause of communication problems with GCM Ethernet NIMs (GCM-ETH-001) is entering incomplete IP addresses in the NIM b...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1165 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

A known cause of communication problems with GCM Ethernet NIMs (GCM-ETH-001) is entering incomplete IP addresses in the NIM block. The NIM block requires full octets (3 digits) in ...

Picard Product_Support
‎2018-09-06 02:49 PM

Issue

A known cause of communication problems with GCM Ethernet NIMs (GCM-ETH-001) is entering incomplete IP addresses in the NIM block. The NIM block requires full octets ( 3 digits) in all four fields of each IP address, e.g. 012.034.056.078

Environment

Network 8000 GCM-86000 series

Network 8000 SIMs, including LNC-100, SIM-CCN, SIM-MTECH, SIM-TRANE, and SIM-YORK (hardware based on the GCM-86000 series)

Ethernet NIM, (Network Interface Module), part number GCM-ETH-001

Cause

The NIM block in the GCM is used to program the NIM hardware, and it requires full octets for all IP addresses.

Resolution

When programming the NIM block for an Ethernet NIM (GCM-ETH-001) installed on a shared Ethernet LAN, the NIM block requires full octets (3 digits) in all four fields of each IP address.

For example, if the network administrator assigns a unique Panel IP Address (PNLIP) of 194.86.47.6, the NIM block should be programmed with PNLIP = 194.086.047.006, where leading zeroes have been added in front of the significant digit(s) to fill each octet with the required three digits. The same rule applies to all IP addresses in the NIM block ( IPMLT, IPSUB, RTRIP, etc.).

Refer to the NIM Networking and Configuration Guide, F-25955-1 for further information on the NIMs.

Note that the IP addresses shown in the manual all have full octets, but the requirement for 3 digits in each field is not explicitly stated. Also note that the UDP Port (UDPPT) address is a hexadecimal number, leave at the default value of ( 1234 hex + NetN hex). For example, if the Network Number of the GCM is 219 decimal, the UDPPT should be (1234 hex + DB hex ) = 130F hex.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2981
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of