Issue
An existing Niagara R2 Enterprise Server was upgraded to 535 but the Vykon Alarm Client (version 2.5) cannot connect to the server.
Environment
Niagara R2
Cause
The Server Name in the Vykon Configuration Utility must be the server's IP address and NOT the station name nor the Windows' Computer Name.
Resolution
See the VAS_InstallationConfiguration Guide for more details.