Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

A Niagara R2 UNC will not keep time accurately. On startup, the standard output window indicates an error loading the timezones.txt file.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • A Niagara R2 UNC will not keep time accurately. On startup, the standard output window indicates an error loading the timezon...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1016 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

A Niagara R2 UNC will not keep time accurately. On startup, the standard output window indicates an error loading the timezones.txt file.

Picard Product_Support
‎2018-09-06 10:34 AM

Issue

A Niagara R2 UNC will not keep time accurately.  The time doesn't just drift a few seconds.  It is jumping around by hours.  Trying to change the time in the Admin Tool does not work.  The following error appears in the standard output window on startup of the UNC:  ERROR: Cannot load /tffs/rel//nre/lib/timezones.txt

---------- Station Starting:   THU FEB 28 14:41:44 2013 ----------
ERROR: Cannot load /tffs/rel//nre/lib/timezones.txt
  java.lang.NumberFormatException
Tridium Niagara Station, r2.301.532.v1 [B_Floor_1]
MESSAGE: ErrorLogService installed [/B_Floor_1/services/ErrorLogService]
GcmCommService Revision 2.304.532.v1
Start service: ControlEngineService [19] ControlEngineService
Start service: UiEngineService [20] UiEngineService
Start service: NotificationService [2] NotificationService
Start service: LogService [21] LogService
Start service: AuditLogService [22] AuditLogService
Start service: ErrorLogService [23] ErrorLogService
Start service: TimeSyncService [26] TimeSyncService
Start service: LonWorksService [28] LonWorksService
Opened lon / LON1
>>> Lon Driver opened!
Start service: GcmCommService [24] GcmCommService
Comm Ports:
  COM1 (serial)
  COM2 (serial)
  COM3 (serial)
  COM4 (serial)
  COM5 (serial)
  COM6 (serial)
Start service: VserialService [25] VserialService
MESSAGE: Station started successfully. (HTTP port=80) [/B_Floor_1]

Environment

Niagara R2

Cause

Corrupt timezones.txt file

Resolution

The timezones.txt file is corrupt.  Copy and paste the contents of this file from a functional UNC and paste it into the problem UNC.

The timezones file can be accessed via the Admin Tool dropdown menu.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 12755
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of