A Niagara R2 UNC station fails to open the lonworks driver and cannot start LON communications.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • A Niagara R2 UNC station fails to open the lonworks driver and cannot start LON communications.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1533 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

A Niagara R2 UNC station fails to open the lonworks driver and cannot start LON communications.

Picard Product_Support
‎2018-09-06 01:54 PM

Issue

Communication to LON controllers is lost.  After a re-start of the station, the following errors appear in the standard output window:

---------- Station Starting:   MON MAY 02 14:53:10 2011 ----------
Tridium Niagara Station, r2.301.529.v1 [test]
MESSAGE: ErrorLogService installed [/test/services/ErrorLogService]
Start service: ControlEngineService [3] ControlEngineService
Start service: UiEngineService [7] UiEngineService
Start service: NotificationService [6] NotificationService
Start service: LogService [5] LogService
Start service: AuditLogService [2] AuditLogService
Start service: ErrorLogService [4] ErrorLogService
Start service: LonWorksService [9] LonWorksService
Error opening driver LON1 java.lang.Exception: Unable to open lonworks driver
***************************************************************
ERROR: Cannot startService [Sys: LonWorksService [9] LonWorksService]
java.lang.IllegalStateException: Unable to open lonworks driver
   at tridiumx.lonworks.services.LonLinkLayer.start (bytecode 143)
   at tridiumx.lonworks.services.LonWorksService.startService (bytecode 12)
   at tridium.foundation.Sys.startServices (bytecode 49)
   at tridium.foundation.Station.startStation (bytecode 63)
   at tridium.foundation.Sys.boot (bytecode 27)
   at tridium.foundation.Sys.bootLocalSns (bytecode 17)
   at tridium.tools.StationMain.bootSns (bytecode 0)
   at tridium.tools.StationMain.doIt (bytecode 352)
   at tridium.tools.StationMain.main (bytecode 10)
   at java.lang.reflect.Method.invoke (Native Method)
   at tridium.nre.Nre.mainImpl (bytecode 271)
   at tridium.nre.Nre.main (bytecode 1)
tridiumx.lonworks.LonException E_LON_COMM_SERVICE_NOT_STARTED
   at tridiumx.lonworks.services.LonCommService.doLonCommSendRequest (bytecode 19)
   at tridiumx.lonworks.services.LonCommService.lonCommSendRequest (bytecode 3)
   at tridiumx.lonworks.services.LonCommService.lonCommSendRequest (bytecode 68)
   at tridiumx.lonworks.util.Neuron.readMemory (bytecode 29)
   at tridiumx.lonworks.util.Neuron.readMemory (bytecode 9)
   at tridiumx.lonworks.util.Neuron.isNMAuthSet (bytecode 32)
   at tridiumx.lonworks.util.Neuron.isNMAuthSet (bytecode 16)
   at tridiumx.lonworks.devices.LocalLonAppDevice.verifyDevice (bytecode 2)
   at tridiumx.lonworks.services.LonWorksService.stationReady (bytecode 28)
   at tridium.foundation.Sys.stationReady (bytecode 23)
   at tridium.foundation.Station.startStation (bytecode 87)
   at tridium.foundation.Sys.boot (bytecode 27)
   at tridium.foundation.Sys.bootLocalSns (bytecode 17)
   at tridium.tools.StationMain.bootSns (bytecode 0)
   at tridium.tools.StationMain.doIt (bytecode 352)
   at tridium.tools.StationMain.main (bytecode 10)
   at java.lang.reflect.Method.invoke (Native Method)
   at tridium.nre.Nre.mainImpl (bytecode 271)
   at tridium.nre.Nre.main (bytecode 1)
MESSAGE: Station started successfully. (HTTP port=80) [test]

These errors follow a short time later:

Freeing transaction from transmit driver, tag is 4
The LonException code is java.lang.Exception: ldvWrite() failed - rc = 6, in transmit driver
Freeing transaction from transmit driver, tag is 5
The LonException code is java.lang.Exception: ldvWrite() failed - rc = 6, in transmit driver

 ... repeated

Environment

Niagara R2 UNC-520-2
Niagara R2 UNC-410-1
(including the -N international versions)

Also applies to obsolete models:  UNC-500, UNC-510, UNC-600, UNC-610

Cause

These errors indicate the Niagara operating system is not communicating to the (on-board) Echelon MIP chip. 

To confirm, run the following test:

  1. Open the running station in Tree View
  2. Go to the Properties of the localLonDevice, specifically the Engineering tab
  3. Blank out the "neuronId" and click Apply
  4. Reboot the UNC
  5. When the station has started successfully, return to the neuronId field and observe the value in the box

If the neuronId field is all zeros, then there is a hardware problem with the Echelon MIP chip.

Resolution

This issue is not field-repairable.

Contact Product Support Services for a return authorization number.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5015
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of