Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

A Niagara R2 / BACnet integration station, running on a computer, can interfere with the WorkPlace Commissioning Tool.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • A Niagara R2 / BACnet integration station, running on a computer, can interfere with the WorkPlace Commissioning Tool.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1230 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

A Niagara R2 / BACnet integration station, running on a computer, can interfere with the WorkPlace Commissioning Tool.

Picard Product_Support
‎2018-09-06 02:29 PM

Issue

A Niagara R2 / BACnet integration station, running on a computer, can interfere with the WorkPlace Commissioning Tool.

Environment

WorkPlace Tech  Commissioning Tool (WPT CT), any revision

I/A series R2 / BACnet integration station running on the same pc as the WPT CT

Cause

Communications port or driver conflict between WorkPlace Tech  Commissioning Tool  and the I/A series R2 / BACnet integration station.

Resolution

A Niagara R2 / BACnet integration station can interfere with the WorkPlace Commissioning Tool (WPCT), by disrupting communications between the WPCT and MNB controllers.

One symptom of this interference is that while the WPCT can find some or all of the MNB controllers, their property sheets will not be fully populated with data.

In such a case, the WPCT might be displaying data from a default template, rather than live data from the controller. As a best practice, check to be sure that the General tab of the device's Properties sheet is populated before going to any other tab. If the Firmware and Application fields of the General tab have not filled in, then the tool is not communicating with the controller, and the other tabs will contain default data, not current values from the controller.

To insure that a Niagara R2 station is not running in the background on the computer follow these steps:

  1. Go to the Computer Management by right-clicking on My Computer
  2. Select Manage from the pull-down menu.
  3. Go to Services and Applications, then Services.
  4. Stop the Niagara service.
  5. Typically, the Niagara service will be configured to start automatically when the computer is rebooted.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3820
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of