7798C does not communicate with a PC or Sub-LAN
  • 7798C does not communicate with a PC or Sub-LAN
  • sesa139513
    sesa139513
  • Tom_Poovey
    Tom_Poovey
‎2018-09-07 12:09 AM
Last Updated: Administrator DavidFisher Administrator ‎2020-10-19 06:30 AM
7798C does communicate with a PC with either cable -- CBL082 or CBL072
TAC INET
I/NET Controllers including the 7798C
Improper Grounding
There must be an earth ground connected to pin #3 of the 24 VAC power connector in order for communications to work correctly.
Click on these pictures for a larger example:
Note: Never use the shield as the ground. Grounding is accomplished by connecting a 14–18 AWG (2.081–0.897 mm2) wire from terminal 3 to true ground.
  • TAC INET
  • 1967
0% helpful (0/1)