Issue
7756 Input Equipment Counts Cross Reference
Environment
7756 Upper Board and Lower Board
Cause
Need to calculate conversion coefficients for a 7756
Resolution
| Point Type | Resistor Type | Resistor Location | Range In Counts |
| 0-5 Volts | None | None | 0-32767 |
| 0-10 Volts | None | None | 0-65535 |
| 2-10 Volts | None | None | 13107-65535 |
| 0-20 mA | 249 ohm, 1/8 W, 0.1% | A | 0-32767 |
| 4-20 mA | 249 ohm, 1/8 W, 0.1% | A | 6553-32767 |
| 0-40 mA | 249 ohm, 1/8 W, 0.1% | A and remove B | 0-65535 |
| Thermistor | 10K ohm, 1/8 W. 0.1% | B | 0-32767 |
| Discrete | 1K ohm, 1/8 W, 0.1% | B | N/A |
| Pulse | 1K ohm, 1/8 W, 0.1% | B | 0-65535 |
| High-speed Pulse | 1K ohm, 1/8 W, 0.1% | B&D | 0-65535 |
| Point Type | Resistor Type | Resistor Location | Range In Counts |
| 0-5 Volts | None | None | 0-4095 |
| 0-10 Volts | None | C | 0-4095 |
| 0-20 mA | 249 ohm, 1/8 W, 0.1% | A | 0-4095 |
| 4-20 mA | 249 ohm, 1/8 W, 0.1% | A | 819-4095 |
| Discrete | 1K ohm, 1/8 W, 0.1% | B | N/A |
| Pulse | 1K ohm, 1/8 W, 0.1% | B | 0-4095 |