Issue
Certain Xenta controllers and I/O modules can accept 10k thermistor temperature inputs.
Product Line
EcoStruxure Building Operation,TAC Vista
Environment
- Xenta 102-AX
- Xenta 420A, Xenta 450A
Cause
The Xenta 102-AX has always used 10k thermistors. Now some of the I/O modules and programmable controllers also have an option for 10k thermistor inputs. A common question is -- what type of 10k thermistors? Type 2? Type 3?
Resolution
- The reason there is no reference to 10k Type 2 or 10k Type 3 is because these are Continuum-specific terms.
- The 10k thermistor that is compatible with Xenta 42XA and 45XA I/O modules are the same that I/NET uses.
- They are Vishay Dale Curve #1.
- View this PDF for the Resistance vs. Temperature Conversion Tables for this thermistor.