Issue
Table needed for linearizing a 10K thermistors for an I/Net 7756 (lower board)
Product Line
TAC INET
Environment
7756 (lower board)
Cause
Thermistors require the use of a look up table to linearize the data.
Resolution
Thermistor Inputs on a PCU 7756 (lower board)
- Enter the Temperature data in °C (First Column - 31 entries)
- Enter the corresponding resistance data in Ohms (Second column - 31 entries)
- Enter the dissipation constant in milliwatts per °C: 2
- Low Temperature : -22.11°F (-30.06°C)
- High Temperature: 247.92°F (119.95°C)
- Point Value in °F: M=0.00412; b=-22.1138
- Point Value in °C: M=0.00228913; b=--30.0632065
Look Up Table:
| °C | Ohms | Current | Self Htg | Adj °C | Adj °F | VDC | Counts | Adj Cts |
|---|---|---|---|---|---|---|---|---|
| 120 | 389 | 0.000481 | 0.045052 | 119.95 | 247.92 | 0.187217 | 1227 | 65535 |
| 100 | 680 | 0.000468 | 0.074521 | 99.93 | 211.87 | 0.318352 | 2086 | 56785 |
| 90 | 917 | 0.000458 | 0.096177 | 89.90 | 193.83 | 0.419987 | 2752 | 52407 |
| 80 | 1258 | 0.000444 | 0.12407 | 79.88 | 175.78 | 0.558714 | 3662 | 48027 |
| 70 | 1753 | 0.000425 | 0.158633 | 69.84 | 157.71 | 0.745767 | 4887 | 43643 |
| 60 | 2489 | 0.0004 | 0.199471 | 59.80 | 139.64 | 0.996477 | 6530 | 39257 |
| 55 | 3045 | 0.000383 | 0.223671 | 54.78 | 130.60 | 1.167114 | 7646 | 37062 |
| 50 | 3602 | 0.000368 | 0.243359 | 49.76 | 121.56 | 1.32407 | 8677 | 34869 |
| 45 | 4368 | 0.000348 | 0.264484 | 44.74 | 112.52 | 1.520045 | 9962 | 32676 |
| 40 | 5326 | 0.000326 | 0.283435 | 39.72 | 103.49 | 1.73757 | 11387 | 30483 |
| 35 | 6691 | 0.0003 | 0.300218 | 34.70 | 94.46 | 2.004374 | 13136 | 28292 |
| 30 | 8056 | 0.000277 | 0.308878 | 29.69 | 85.44 | 2.230837 | 14620 | 26104 |
| 28 | 8777 | 0.000266 | 0.311174 | 27.69 | 81.84 | 2.337168 | 15317 | 25229 |
| 26 | 9572 | 0.000255 | 0.312351 | 25.69 | 78.24 | 2.44533 | 16025 | 24355 |
| 25 | 10000 | 0.00025 | 0.3125 | 24.69 | 76.44 | 2.5 | 16384 | 23918 |
| 24 | 10450 | 0.000244 | 0.312349 | 23.69 | 74.64 | 2.555012 | 16744 | 23481 |
| 22 | 11420 | 0.000233 | 0.311127 | 21.69 | 71.04 | 2.665733 | 17470 | 22608 |
| 20 | 12490 | 0.000222 | 0.308669 | 19.69 | 67.44 | 2.77679 | 18198 | 21735 |
| 18 | 13680 | 0.000211 | 0.304953 | 17.70 | 63.85 | 2.888514 | 18930 | 20863 |
| 16 | 15000 | 0.0002 | 0.3 | 15.70 | 60.26 | 3 | 19661 | 19992 |
| 14 | 16470 | 0.000189 | 0.29383 | 13.71 | 56.67 | 3.111069 | 20388 | 19121 |
| 12 | 18090 | 0.000178 | 0.286579 | 11.71 | 53.08 | 3.220007 | 21102 | 18250 |
| 10 | 19900 | 0.000167 | 0.278241 | 9.72 | 49.50 | 3.327759 | 21808 | 17380 |
| 8 | 21920 | 0.000157 | 0.268921 | 7.73 | 45.92 | 3.433584 | 22502 | 16510 |
| 6 | 24180 | 0.000146 | 0.258715 | 5.74 | 42.33 | 3.537156 | 23181 | 15641 |
| 0 | 32660 | 0.000117 | 0.224329 | -0.22 | 31.60 | 3.827942 | 25086 | 13035 |
| -4 | 36200 | 0.000108 | 0.211999 | -4.21 | 24.42 | 3.917749 | 25675 | 11293 |
| -10 | 55340 | 0.0000765 | 0.162028 | -10.16 | 13.71 | 4.234772 | 27753 | 8694 |
| -14 | 69000 | 0.0000633 | 0.138199 | -14.14 | 6.55 | 4.367089 | 28620 | 6957 |
| -20 | 97130 | 0.0000467 | 0.105789 | -20.11 | -4.19 | 4.533277 | 29709 | 4350 |
| -30 | 177200 | 0.0000267 | 0.063207 | -30.06 | -22.11 | 4.732906 | 31017 | 0 |
This spreadsheet is for a thermistor rated at 10,000 ohms at 25°C.
- Install a 10K Ohm Resistor in the "B" terminal (consult the TCON for the controller you are using for details)
- This look up table program is based on using 31 entries
- The data points do not have to be evenly spaced
Click here to download this in pdf format.
For the look up table to the 7716, 7718, 7728 and a 7756 (upper board), see 10k Thermistor Look Up Tables for a 7716, 7718, 7728 and a 7756 (upper board).