Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
fire pump feeder breaker
Ask the Community
Ask questions, get advice from experts and peers on Digital Automation & Energy Management.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
It is not clear why the nominal rating of the breaker be 800 A?
Since only short circuit protection is required, why can't the breaker(OCPD) trip setting for short circuit be set at the required value rather than having a large sized breaker?
Code requirement is for the OCPD sizing, which the Short circuit rating here, not the Overload rating of the breaker!