Posted: 2023-09-22 07:43 AM
hello
breaker 400A with 80% if i ajuste the sensor to 80% what the amper that ican support
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-25 06:21 AM
Hi,
depend the model of breaker. If only have the Ir setting is only realize a simple operation:
Nominal current breaker * Ir. THis is, Ir=0.8 (80%) and the breaker nominal current 400A. The adjust is 400 * 0.8 = 320A.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-27 04:46 AM
thank you, is the same thing if we have a breaker with 80% rated if we set Ir= 0,8 the breker nominal curent 400A the adjuste will be 400*0,8 + = 320 a or it is another thing thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-30 09:15 AM
Farouk,
that is correct.
regards,