Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-2110:58 AM
Thermal Magnetic Circuit Breaker NSX with TMD Trip Unit (Maximum permitted Zsd
How do I work out the Zs for this MCCB at 250A the measured Zs value I have is 0.29 ohms am I correct in saying it would be 0.87 ohms Rated Voltage to earth with Cmin (230 Vac x 0.95 ) = 218.5 using this formula The earth fault loop impedance Zs (Ohms) = Rated Voltage to earth (Vac ) / Device opperating Current (A)