The objects in the Sigma graphical interface have not changed with the refresh of the system manager object

Ask the Community

Ask questions, get advice from experts and peers on Digital Automation & Energy Management.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Support
  • Ask the Community
  • The objects in the Sigma graphical interface have not changed with the refresh of the system manager object
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
33
MikaelKrantz
Kirk MikaelKrantz Kirk
7
Omaelk
Janeway Omaelk
3
DavidFisher
Administrator DavidFisher Administrator
1
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Ask the Community
Anonymous user
Not applicable

Posted: ‎2021-01-04 11:00 PM . Last Modified: ‎2021-01-04 11:02 PM

0 Likes
2
1424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-04 11:00 PM . Last Modified: ‎2021-01-04 11:02 PM

The objects in the Sigma graphical interface have not changed with the refresh of the system manager object

1.png2.png3.pngIt will be refreshed only when the "interval for complete refresh of objects" (60Mins) of "communication Times" arrives.

 

How can the above problems be solved? Make the Sigma Graphics interface change as the value changes

 

 

I have set the following settings to the lowest value:

 

System setup > controller items > communication times > main network:

Interval for server and controller handshaking (minutes = 5)

interval for complete refresh of object (minutes = 60)

 

Object Tolerance: 0.05 (for Tempeature)

  • Tags:
  • english
  • sigma
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2021-01-05 04:56 PM

0 Likes
0
1408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-05 04:56 PM

You firstly need to understand the event based mechanism that Sigma uses for graphics. In short when a graphic is opened a list of all of the points(objects) that are to be displayed on the graphic are sent to the OSN(S) this is called a PIT(Points of Interest to the Terminal) list, this list also contains information about how much a value must change by before the OSN updates the graphic(tolerance). Initially the OSN provides the server the value of all the points requested so that the graphic can be populated, thereafter as values change by more than the tolerance the OSN updates the server, in addition the entire set of values is updated every 2 minutes regardless of change. This list is maintained in the OSN until the graphic is closed and the OSN is notified that these points are no longer required and the PIT list is removed or amended.

The complete refresh interval is a failsafe so that is an OSN is reset and it's PITlist is lost the Server will resubscribe everything at this defined interval.

 

What you need to look at is if the object is correctly registered in the controller and if updates are being sent.

 

Right click on the server icon and select Show Requested Objects

 

ShowUpdates.jpg

 

This should show you the objects and their status including number of updates

 

ReqObjectsSummary.jpg

 

I'd recommend that you start a support case with your local Schneider Electric organisation if this needs to be investigated further.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

DavidChild
Sisko DavidChild Sisko
Sisko

Posted: ‎2021-01-29 02:51 AM . Last Modified: ‎2021-01-29 03:06 AM

1 Like
0
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-01-29 02:51 AM . Last Modified: ‎2021-01-29 03:06 AM

Hi @Anonymous user 

 

I've received a support case for this and have followed this through the Support channel.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of