STR-150 & Return Sensor with Xenta 122-FC

Ask the Community

Ask questions, get advice from experts and peers on Digital Automation & Energy Management.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Support
  • Ask the Community
  • STR-150 & Return Sensor with Xenta 122-FC
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
33
MikaelKrantz
Kirk MikaelKrantz Kirk
7
Omaelk
Janeway Omaelk
3
chris_clerc
Administrator chris_clerc Administrator
2
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Ask the Community
digvijay
Lieutenant JG digvijay
Lieutenant JG

Posted: ‎2019-09-09 11:31 PM . Last Modified: ‎2020-12-02 04:31 AM

1 Like
7
3894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-09-09 11:31 PM . Last Modified: ‎2020-12-02 04:31 AM

STR-150 & Return Sensor with Xenta 122-FC

Hi All,

 

I have a scenario in which an STR-150 thermostat and a return sensor are to be connected to a Xenta-122FC. I need to run the Xenta controller based on the return sensor temperature value and setpoint to be given from server. And have to export the temperature & setpoint values from STR-150 to other controller(to be used for other purpose). Does anyone know how to achieve this? Which of the Xenta terminals the thermostat and return sensor should be connected? How should be the bindings be done?

  • Tags:
  • 122FC
  • STR150
  • xenta
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Omaelk
Janeway Omaelk
Janeway

Posted: ‎2019-09-10 04:46 AM

1 Like
0
3886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-09-10 04:46 AM

Hello @digvijay , welcome on Exchange community. I add @MikaelKrantz to the thread as he may be able to help you with your issue. 

 

PS: do not hesitate to use the search bar with key words to check if your issue was not already discussed somewhere in the community 😉 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

MikaelKrantz
Kirk MikaelKrantz Kirk
Kirk

Posted: ‎2019-09-10 06:58 AM

1 Like
5
3882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-09-10 06:58 AM

The TAC Xenta 122-FC device has to be configured with the ZBuilder tool, that is an LNS PlugIn software.

Here you can select what input you should use for the temp, and under Configuration tab, Application, Special Functions, there is a checkbox for selecting Do not use space temperature from STR150.

Reply

Link copied. Please paste this link to share this article on your social media post.

digvijay
Lieutenant JG digvijay
Lieutenant JG

Posted: ‎2019-09-10 07:24 AM

In response to MikaelKrantz
1 Like
2
3876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-09-10 07:24 AM

Thanks Mikael! How can I export the STR-150 Temperature and Setpoint values in this situation?
Reply

Link copied. Please paste this link to share this article on your social media post.

MikaelKrantz
Kirk MikaelKrantz Kirk
Kirk

Posted: ‎2019-09-10 07:36 AM

In response to digvijay
1 Like
1
3872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-09-10 07:36 AM

Not from the sensor, but from the controller.

nvoSpaceTemp

nvoEffectSetpt

Reply

Link copied. Please paste this link to share this article on your social media post.

digvijay
Lieutenant JG digvijay
Lieutenant JG

Posted: ‎2019-09-11 10:33 PM

In response to MikaelKrantz
1 Like
0
3857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-09-11 10:33 PM

Let me check on the site for the values on these NVOs and get back to you. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Waqas_Shahid
Ensign Waqas_Shahid
Ensign

Posted: ‎2025-05-26 12:06 AM

In response to MikaelKrantz
0 Likes
1
142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-26 12:06 AM

Is there any option for the selection of either STR-150 or temperature sensor once controller is added under SBO under these sub folder as my previous selection in this controller on return sensor now I want to replace it with STR-150 and I don't have LNS or Tac vista.

1000184332.jpg

 

Reply

Link copied. Please paste this link to share this article on your social media post.

MikaelKrantz
Kirk MikaelKrantz Kirk
Kirk

Posted: ‎2025-05-26 12:53 AM

In response to Waqas_Shahid
0 Likes
0
141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-26 12:53 AM

What type of controller du you have?

STR150 only talk to the TAC Xenta 100 series.

Or, do you think about STR350, which are using SNVT?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of