Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

MICOM Transformer Differential

Ask the Community

Ask questions, get advice from experts and peers on Digital Automation & Energy Management.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Support
  • Ask the Community
  • MICOM Transformer Differential
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
33
MikaelKrantz
Kirk MikaelKrantz Kirk
7
Omaelk
Janeway Omaelk
3
DavidFisher
Administrator DavidFisher Administrator
1
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Ask the Community
Anonymous user
Not applicable

Posted: ‎2021-04-19 06:23 AM

0 Likes
1
1265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-19 06:23 AM

MICOM Transformer Differential

Dears,

 

I am working on a project opportunity and the customer needs a special requirement for a 7 winding transformer feeder used for a 36-pulse converter (VSD with two transformers each transformer with 3 secondary winding supplying the VSD).

as per the attached snapshot; my query/ clarification to vouch for the applicability of this requirement using MICOM P64x, MICOM P63X series.

Consequently, as per the Attached snapshot from the customer's SLD, it is clearly indicated that 21 current inputs are required (1 set of CTs on the primary side of the transformer & 6 sets of CTs on the secondary side of the transformer) but as per the MICOM P645, the maximum current inputs are 15 which means that a 5 winding transformer is the maximum that can be used ( snapshot from MICOM P645 is attached FYR).

So, thanks to advise /confirm regarding this query or if there is a possibility of using summing interposing CTs to achieve this requirement similar to that of ABB relay RET670.

 

Awaiting your reply at your earliest convenience.

 

Thanks in advance & Best regards,

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Anonymous user
Not applicable

Posted: ‎2021-04-20 08:21 AM

0 Likes
0
1255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-20 08:21 AM

Thanks to Mr. Rudolf Simon for his usual & appreciable support for solving the case. His reply has been attached.

 

Currently, Thanks for supporting us if there is a similar project or case that faced anyone where interposing & summation CTs has been used to achieve such requirement whether for 7 windings transformer equipped with 21 current inputs are required (1 set of CTs on the primary side of the transformer & 6 sets of CTs on the secondary side of the transformer) or even less than the mentioned winding's number but equipped with summation & interposing CTs. If so, thanks to provide us with the project reference & the equivalent documents.

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now