Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Lonwork device discovery

Ask the Community

Ask questions, get advice from experts and peers on Digital Automation & Energy Management.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Support
  • Ask the Community
  • Lonwork device discovery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
35
chris_clerc
Administrator chris_clerc Administrator
7
MikaelKrantz
Kirk MikaelKrantz Kirk
7
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Ask the Community
Start a Topic
Solved
nagaralesb
Crewman nagaralesb
Crewman

Posted: ‎2024-03-10 04:27 AM

0 Likes
2
1144
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-10 04:27 AM

Lonwork device discovery

Dear Team,

 

 I am using Automation Server (1.5), I am trying to discover LON device (Kamstrup BTU meter), but not able to discover.

Below steps followed,

  1. Opened Workstation and locate Automation server.
  2. Left-click on the Automation server to select it.
  3. Select the "Discovery Devices" tab.
  4. In the "Select device Type" drop-down list, click to expand the options and choose "Lonworks".
  5. Right-click on the "Devices" folder.
  6. From the context menu, select "Scan network for devices".

This 6th point (Scan network for devices is not showing). Only Activate listen to service pin, Deactivate listen to service pin & Clear found devices showing.

 

Please help me to discover lonwork device.

 

Regards,

Sachin

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-03-11 05:17 PM

0 Likes
0
1107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-11 05:17 PM

@nagaralesb as @MikaelKrantz noted SBO version 1.5 is 10 years old and really should be upgraded to a supported version.

 

The behaviour that you are seeing is completely normal in this version, service pin is the way that LON devices were discovered. See section 57.5 of the SBO 1.5 Technical Reference Guide

 

To discover a LonWorks device
1. In WorkStation, in the System Tree pane, select the server that is connected to the device you want to discover.
2. Click the Device Discovery view.
3. In the Select device type box, select LonWorks.
4. Select the Devices folder.
5. On the Actions menu, click Activate listen to service pin.
6. Press the service pin on the physical device.
7. In the Device Discovery view, ensure that the LonWorks device is displayed in the Devices folder. This may take up to 5 seconds.
8. On the Actions menu, click Deactivate listen to service pin.

9. Drag the discovered service pin (device) to the System Tree pane:
• Drag to an existing device to associate it with the discovered physical
device.
• Drag to the LonWorks network to create the device.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
MikaelKrantz
Kirk MikaelKrantz Kirk
Kirk

Posted: ‎2024-03-11 01:10 AM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-11 01:10 AM

Why using such old version?

Should recommend to upgrade to 1.9, at least.

Reply

Link copied. Please paste this link to share this article on your social media post.

CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2024-03-11 05:17 PM

0 Likes
0
1108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-11 05:17 PM

@nagaralesb as @MikaelKrantz noted SBO version 1.5 is 10 years old and really should be upgraded to a supported version.

 

The behaviour that you are seeing is completely normal in this version, service pin is the way that LON devices were discovered. See section 57.5 of the SBO 1.5 Technical Reference Guide

 

To discover a LonWorks device
1. In WorkStation, in the System Tree pane, select the server that is connected to the device you want to discover.
2. Click the Device Discovery view.
3. In the Select device type box, select LonWorks.
4. Select the Devices folder.
5. On the Actions menu, click Activate listen to service pin.
6. Press the service pin on the physical device.
7. In the Device Discovery view, ensure that the LonWorks device is displayed in the Devices folder. This may take up to 5 seconds.
8. On the Actions menu, click Deactivate listen to service pin.

9. Drag the discovered service pin (device) to the System Tree pane:
• Drag to an existing device to associate it with the discovered physical
device.
• Drag to the LonWorks network to create the device.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore