I get below message when try downloading Visio file into the MNL-V1RV3 Controller. Why it said the device is not compatible?
error message
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-07 10:09 PM
Most likely you have LON communication issues and WP-TECH is unable to correctly receive the device type.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-07 10:09 PM
Most likely you have LON communication issues and WP-TECH is unable to correctly receive the device type.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-13 05:33 PM
Yes, you are correct. There was no LON extension files in the WP Tech folder. Thanks for pointing out.