Hour Meter on Altivar 61 not working

Solutions for Motor Management

Get support to configure, troubleshoot, update or upgrade your motor management solution built with Altivar variable speed drives and Tesys devices to start, control, protect and monitor Low Voltage and Medium Voltage motors and loads, covering direct start, soft start and variable speed control.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Solutions for Motor Management
  • Hour Meter on Altivar 61 not working
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BJacqz
Commander BJacqz Commander
48
LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
16
PriscilaCunha22
Lieutenant JG PriscilaCunha22 Lieutenant JG
12
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
9
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Solutions for Motor Management
Solved
TCRWater
TCRWater
Cadet

Posted: ‎2023-03-27 12:44 PM . Last Modified: ‎2023-03-31 03:55 AM

0 Likes
2
1617
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-27 12:44 PM . Last Modified: ‎2023-03-31 03:55 AM

Hour Meter on Altivar 61 not working

Hello,

I have an Altivar 61 running a deep well submersible pump.  It's working fine however the hour meter has stopped working on it.  The meter has stopped at 65535 hrs.  This happened a couple years ago.  It shows 65535 on both the remote screen (on the outside of the panel) and the main component (red digits, inside the panel).  I just found this community after asking others for help so I hope the answers are here!!

 

I have no idea where to start so any help would be appreciated.  Thank you kindly!!

Attachments
Labels
  • Labels:
  • Low Voltage AC Drives
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bosswaffle
Lt. Commander Bosswaffle
Lt. Commander

Posted: ‎2023-03-27 01:31 PM . Last Modified: ‎2023-03-31 05:25 AM

1 Like
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-27 01:31 PM . Last Modified: ‎2023-03-31 05:25 AM

65535 happens to be the maximum value of an unsigned 16bit integer! It would apear that you have exceded the capacity this drive can count up too. Interestingly, 65535 hours is 2,730.6 days or 7.48 years. considering that happened years ago, your drive has performing quite admibrably! 

 

It seems that you need to reset that counter (and make note of how many times you reset it if you ever need to reset it agian) or check to see if newer firmware uses a 32bit integer to count run hours.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Bosswaffle
Lt. Commander Bosswaffle
Lt. Commander

Posted: ‎2023-03-27 01:31 PM . Last Modified: ‎2023-03-31 05:25 AM

1 Like
0
1610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-27 01:31 PM . Last Modified: ‎2023-03-31 05:25 AM

65535 happens to be the maximum value of an unsigned 16bit integer! It would apear that you have exceded the capacity this drive can count up too. Interestingly, 65535 hours is 2,730.6 days or 7.48 years. considering that happened years ago, your drive has performing quite admibrably! 

 

It seems that you need to reset that counter (and make note of how many times you reset it if you ever need to reset it agian) or check to see if newer firmware uses a 32bit integer to count run hours.

Reply

Link copied. Please paste this link to share this article on your social media post.

LeoLazzaro
Lieutenant LeoLazzaro Lieutenant
Lieutenant

Posted: ‎2023-03-30 09:16 AM

1 Like
0
1585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-30 09:16 AM

Dear both :  Bosswaffle is righ almost all of our variable are 16 bit integer in ATV61 or 71 . There is a procedure to reset these values. I recommend you to contact your local customer care center to do it because you need to  access hidden parametrization   and you need someone to guide you to dont make a mistake . Other possibility is to contact Schneider Electric Service team to do it.

Thank you in advance

B.R.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of