Webhooks in IT Expert

Administration

How to manage your EcoStruxure IT Expert organization including users, groups, subscriptions, and alarm notifications, and Gateways

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Expert
  • Configuration
  • Administration
  • Webhooks in IT Expert
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Webhooks in IT Expert
  • Video: Manage users in IT Expert
  • Video: Inviting users to join your organization in...
  • IT Expert permissions
  • Video: Administrator access for Customer Success M...
  • Video: Add a partner to your organization in IT Ex...
  • Webhooks in IT Expert
  • Video: Manage users in IT Expert
  • Video: Inviting users to join your organization in...
  • IT Expert permissions
  • Video: Administrator access for Customer Success M...
  • Video: Add a partner to your organization in IT Ex...

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Administration
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1982 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Webhooks in IT Expert

Sisko JLehr Sisko
‎2025-04-10 03:35 AM

 

Webhooks seamlessly integrate external applications and services with EcoStruxure IT.

Get real-time data updates, trigger specific actions based on events, automate workflows, and enhance collaboration between different systems.

 

Administrators can configure webhooks to manage the incident escalation process in platforms such as ServiceNow, X-matters, MoogSoft, or on local servers.

 

An IT Expert subscription is required.

 

ITE Webhook schema

 

 

About webhooks

 

Webhooks are automated requests sent from one application or service to another when a specific event occurs.

 

An application subscribes to events to receive notifications when those events happen. The webhook subscription describes the event the application wants to receive and the destination where webhooks should be sent.

 

 

Configure webhooks in EcoStruxure IT

 

Add destinations

 

Go to Administration > More > Webhooks.

 

Add one or more destinations and then add subscriptions. Subscriptions must be associated with a valid destination.

 

Click New destination.

 

ITE webhooks 1.png

 

Specify the Destination name and the URL starting with https://

 

Select the Authentication method, Basic or Token.

 

For Basic authentication, enter the Username and Password.

For Token authentication, enter the Security token.

 

Click Save.

 

ITE webhooks create destination 1.png

Add subscriptions

 

Click New subscription.

 

ITE webhooks create subscription 1.png

 

Specify the Subscription name and select the Event type, API version, and the Destination.

At this time, only the ALARM event type and 1.0.0 API version are available.

 

Select a destination from the dropdown list, or click New to create a new destination.

Note: Multiple subscriptions can point to a destination.

 

When you select an existing destination, you can click Info to update it. You can modify its name and URL or reset its authentication. Click Update to save your changes.

 

Click Save. 

 

ITE webhooks create subscription 2.png

 

Modify webhook settings

 

Click the dots next to each entry to see available actions.

 

Destinations

 

  • Edit
  • Delete: You cannot delete a destination when a subscription is associated with it.

 

Subscriptions

 

  • Test configuration: Sends multiple requests to the destination with data that can be used by the subscription.

    After a subscription begins sending events, view the delivery log to verify. If an event cannot be delivered after several retries, it will be logged as failed.

  • Delivery logs: View the log for the subscription including the Timestamp, Request start time, End time, Duration, Destination URL, Authentication method, and Description. The delivery log cannot be exported at this time.
  • Edit
  • Delete

 

ITE webhooks 2.png

 

Attachments
ITE_WEBHOOK_SCHEMA.zip
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

Comments
DrewWatson
DrewWatson
Cadet
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-04-14 07:29 AM

Will teams webhooks be supported? 

JLehr
Sisko JLehr Sisko
Sisko
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-04-16 11:03 AM

Hi @DrewWatson,

 

Engineering verified that Teams webhooks are not supported.

 

Teams uses its own JSON formatted objects with predefined fields, which IT Expert does not support.

Since Teams needs a special message format, direct integration won't work; you'll need to transform the data.

You might consider using a message adaptation service to receive messages from IT Expert, transform them into the format Teams expects, and then forward the adapted message to Teams.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore