Plant Scada and Micrologix

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Plant Scada and Micrologix
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Lt. Commander olivier_vallee
29
Oncom
Commander Oncom
6
BevanWeiss
Spock BevanWeiss
2
RoozeeR
Lt. Commander RoozeeR Lt. Commander
2
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to AVEVA Plant SCADA Forum
ryanhuynh
Ensign ryanhuynh
Ensign

Posted: ‎2025-07-10 11:36 PM

0 Likes
2
93
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-10 11:36 PM

Plant Scada and Micrologix

Hi guys,

I'm a bit new to Plant Scada so might be something silly that I missed. 

I'm trying to set up tags from a micrologix 1400, they are O:0.4 , F8:10. THey are still displaying 0 with a good quality on run time. 

Any insight? Pretty sure plc is online and tags is reading value because I checked it with another Scada software. 

Thanks

ryanhuynh_0-1752215460599.png

ryanhuynh_1-1752215494205.pngryanhuynh_2-1752215515378.pngryanhuynh_3-1752215538885.png

 

Labels
  • Labels:
  • Plant SCADA Studio
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2025-07-15 04:54 PM

1 Like
0
62
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-15 04:54 PM

Hi @ryanhuynh,

I assume you are using the Plant SCADA driver ABMLXEIP?

I'd suggest enabling logging for the driver, by setting the following Citect.ini parameters:

[ABMLXEIP]
DebugLevel=ALL
DebugCategory=ALL

 

The events generated by the ABMLXEIP driver are logged in the following Plant SCADA syslog file:

syslog.IOServer.<Cluster name>.<IO Server name>.dat

This file is located in the directory specified by the Citect.ini parameter [CtEdit]Logs. By default, this location will be:

%PROGRAMDATA%\AVEVA Plant SCADA <VersionNumber>\Logs

The size of the syslog file and its rollover process is configured via the [Debug]SysLogSize and [Debug]SysLogArchive INI parameters

 

Look for the Channel (Port) and Unit (IODevice) coming online. Are there any errors in the log?

 

Let us know how you go.

 

Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

ryanhuynh
Ensign ryanhuynh
Ensign

Posted: ‎2025-07-28 07:11 PM

0 Likes
0
23
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-28 07:11 PM

Thanks Oliver,
My case, I needed to restart the IO server to initiate the connection. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.