A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-25 09:46 PM
i need to add a process analyst window in scada screen with permanent pens. That means every time the scada runs, the process analyst window should be working without adding the tags again and again. How can i do that?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-26 10:58 PM
Hello Apeiris
You have different options.
1- Function ProcessAnalystSetPen
See also
2- Function TrnSetPen
see also
https://gcsresource.aveva.com/plantscada/WebHelp/plantscada2023/Content/Cicode/Trend_Functions.html
3 - Configuring the Pen Data Connection
see also
Remember: To access AVEVA online help it is necessary to have an account on the AVEVA website
Good luck!
Ricard
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-19 04:57 PM
There are many ways to load Pens and keep them
As suggested above, you can choose to use cicode to manage/load the Trend Pens or save loaded pens as Process Analyst Views (.pav) as files. Then load the pav files.
Additionally, in graphics builder, select the PA Object, under Access | Identification
TICK the Checkbox Persistence - persist ActiveX between page Transitions
This will ensure any trends that you load in runtime is persisted upon page changes.
Hope this helps.