Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to Change the linked "Relié" Option to "Non" in CitectSCADA Tag Editor

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • How to Change the linked "Relié" Option to "Non" in CitectSCADA Tag Editor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
olivier_vallee
37
Oncom
Oncom
6
stuartm
stuartm
2
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to AVEVA Plant SCADA Forum
Start a Topic
Solved
oualid
oualid
Explorer

Posted: ‎2024-12-13 02:21 PM

0 Likes
4
1510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 02:21 PM

How to Change the linked "Relié" Option to "Non" in CitectSCADA Tag Editor

In the CitectSCADA Tag Editor, When the "Relié" option is set to "Oui" (Yes), the tag becomes locked, and editing is restricted. However, when the "Relié" option is "Non" (No), the tag is editable as in the attached images.

For cases where the "Relié" option is "Oui," how can we change it to "Non" to enable editing of the tag?

Looking forward to guidance on making tags editable while preserving their functionality.

Attachments
Labels
  • Labels:
  • Industrial Graphics
  • Plant SCADA Anywhere
  • Scripting - Cicode
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
olivier_vallee
olivier_vallee
Mentor

Posted: ‎2025-02-02 04:21 PM

1 Like
1
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-02 04:21 PM

Hi @oualid ,

It is difficult to assist you over a forum post. It requires inspecting the actual configuration in the project and making further suggestions.

I'd recommend reaching out to Technical Support to discuss your setup and the best path forward.

As long as you have a project backup, you can safely experiment with different changes and see what impact it has. Obviously do this on a non-production system, or VM.

The main thing you need to be concerned about is triggering a tag refresh and overwriting changes you previously made.

Let us know how you go with it.

Kind regards

Olivier

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
olivier_vallee
olivier_vallee
Mentor

Posted: ‎2024-12-17 03:15 PM

1 Like
1
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-17 03:15 PM

Hi @oualid,

It looks like you are using quite an old version of Citect!

What happens when the record isn't able to be edited, means that the tag is linked to tag import or equipment template:

"The Linked field in the status line of the Variable Tags form reads either Yes or No and indicates whether or not the variable tag is linked to an external data source. When you program an I/O Device using software other than Vijeo Citect, an external data source is used to store tag data. Linked variable tags are updated whenever external tag data changes, meaning you are not required to enter the information again in Vijeo Citect."

 

So I think you must unlink it to be able to edit it, but be warned that any change you make in the external data source won't be synchronised back to this tag anymore.

 

Another option is to edit the Variable.dbf using Excel and the DBF Editor plugin, but again, if you make changes directly, they might be overwritten by the external data source when the sync occurs.

 

It might be helpful to talk to the Engineer who originally build your SCADA system to get more insight into the setup and expected work flow to make changes.

 

Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

oualid
oualid
Explorer

Posted: ‎2024-12-29 01:29 PM

In response to olivier_vallee
0 Likes
0
1449
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-29 01:29 PM

Thank you for your detailed explanation. Unfortunately, consulting the original engineer is not an option. Could you please advise if there's a method to identify the tag import, equipment template, or external data source the tag is linked to? Additionally, is there a safe and recommended process to unlink the tag without disrupting the system?

Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
olivier_vallee
Mentor

Posted: ‎2025-02-02 04:21 PM

1 Like
1
1382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-02 04:21 PM

Hi @oualid ,

It is difficult to assist you over a forum post. It requires inspecting the actual configuration in the project and making further suggestions.

I'd recommend reaching out to Technical Support to discuss your setup and the best path forward.

As long as you have a project backup, you can safely experiment with different changes and see what impact it has. Obviously do this on a non-production system, or VM.

The main thing you need to be concerned about is triggering a tag refresh and overwriting changes you previously made.

Let us know how you go with it.

Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

oualid
oualid
Explorer

Posted: ‎2025-02-05 02:51 AM

In response to olivier_vallee
1 Like
0
1360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-05 02:51 AM

Hi @olivier_vallee.
Thank you for your suggestions. I have been experimenting with different changes on a non-production system, ensuring that a backup is in place, and so far, nothing adverse has occurred. I appreciate your guidance and will proceed cautiously, especially regarding tag refresh and potential overwrites.

Best regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore