Having trouble connecting to Plant Scada OPC UA server from UAexpert
AVEVA Plant SCADA Forum
A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Having trouble connecting to Plant Scada OPC UA server from UAexpert
olivier_vallee
Lt. Commander olivier_vallee
31
Oncom
Commander Oncom
6
BevanWeiss
Spock BevanWeiss
2
RoozeeR
Lt. Commander RoozeeR Lt. Commander
2
Back to AVEVA Plant SCADA Forum
ryanhuynh
Ensign ryanhuynh
Ensign
Posted: ‎2025-06-29 09:41 PM
419
Hi guys,
I'm trying to connect a Plant Scada ver 8.4 OPC UA server to UAxpert but having connection reset timeout
I've also checked the port of the opc server is open. Not sure if I did anything wrong. Any insights would be appreciated!
  • Servers - Clients
Replies 13
olivier_vallee
Lt. Commander
Posted: ‎2025-07-01 02:19 PM
2
413
Hi @ryanhuynh
Definitely check out the help and prerequisites for OPC UA Server here:
https://docs.aveva.com/bundle/plant-scada/page/1037376.html
Make sure SMS is configured, Encryption is enabled for Plant SCADA (the Connectivity Service and IO/Server require encrypted communications) and Plant SCADA is running as a Windows Service.
Restart the Connectivity Service as well, just in case any settings need to take effect.
ryanhuynh
Ensign ryanhuynh
Ensign
Posted: ‎2025-07-02 12:22 AM
In response to olivier_vallee
404
Thanks for the reponse Oliver,
It was the firewall issue. But I still can't see any I/O or tags from Plant scada on browsing of UAexpert. Did I miss any steps?
olivier_vallee
Lt. Commander
Posted: ‎2025-07-02 02:05 PM
In response to ryanhuynh
Sounds like you are getting closer. I would recommend checking the syslog.dat for the IOServer to see if any warnings or errors there. It seems the connection between Connectivity Server and the IOServer is offline. Check that security is enabled. Also check the Log Viewer (Operations Control Management Console) for any messages relating to the Connectivity Service.
ryanhuynh
Ensign ryanhuynh
Ensign
Posted: ‎2025-07-02 03:43 PM
No warning or error on syslog so far. I couldn't see any operation control management console in start menu of aveva group, weird!
WHere can I check the security you mentioned?
Thanks Oliver
ryanhuynh
Ensign ryanhuynh
Ensign
Posted: ‎2025-07-02 03:50 PM
Also,
Here is my configurator setting screen. I haven't enabled the ecrypted communication yet, based on my understanding, you don't have to enable this to browse tags, do you?
olivier_vallee
Lt. Commander
Posted: ‎2025-07-02 10:54 PM
I forgot that Plant SCADA 8.40 doesn't have a shortcut for (Operations Control Management Console), but you can load it by runnning the program aaLogViewer.exe found in the folder C:\Program Files (x86)\Common Files\ArchestrA
With regards to Encryption on the OPC UA Server config, you can leave it unticked or unsecure. That is for the OPC Client to OPC Server connection, it can be unsecure for now. It shouldn't have an impact on this issue.
Check that Encryption is enabled for Plant SCADA, and that it is running as a Windows Service. When you see Runtime Manager, it should say "Service Mode" in the window title.
Obviously runtime should be online, and Networking Enabled (citect.ini - [LAN]TCPIP=1).
If you are still stuck, I recommend reaching out to Customer Support and do a live session to debug this further.
Kind regards
Olivier
ryanhuynh
Ensign ryanhuynh
Ensign
Posted: ‎2025-07-07 11:06 PM
Unsure why my reply hasn't been uploaded yet.
Anyway, thanks Oliver. Here is error in the logviewer. What is your opinion?
ryanhuynh
Ensign ryanhuynh
Ensign
Posted: ‎2025-07-07 11:16 PM
olivier_vallee
Lt. Commander
Posted: ‎2025-07-08 05:10 PM
Hi @ryanhuynh
Not sure why the reply was held up, perhaps there is a delay in "moderation" side?
Thanks for sharing more details. That error was reported internally during testing before.
I had a quick look at Plant SCADA 2023 latest patch, and there are a lot of bug fixes in the OPC UA Server component.
I would recommend to apply the June 2025 Patch (available on AVEVA Support Website) on top of your test system to see if it resolves this browse issue.
You could also experiment with toggling the setting "Disable properties and extensions" on the OPC UA Server on the Configurator.
Let me know how it goes.
ryanhuynh
Ensign ryanhuynh
Ensign
Posted: ‎2025-07-09 11:18 PM
Thanks Oliver. Good to know. Probably need to schedule for a patch update somedays.
ryanhuynh
Ensign ryanhuynh
Ensign
Posted: ‎2025-07-10 06:58 PM
295
Hi Oliver,
Probably I can't patch it anytime soon due to operation.
But I tried toggle off and on and hit configure button. I found this, please have a look at attachment.
olivier_vallee
Lt. Commander
Posted: ‎2025-07-13 03:22 PM
It looks like Encryption is not enabled. The connection between the IOServer (which is the source of the IO Data) and the Connectivity Service must be encrypted. As previously stated, this means:
- Make sure SMS is configured
- Encryption is enabled for Plant SCADA (the Connectivity Service and IO/Server require encrypted communications)
- Plant SCADA is running as a Windows Service
ryanhuynh
Ensign ryanhuynh
Ensign
Posted: ‎2025-07-14 03:22 PM
Thanks Oliver. I'll set my laptop as IO server and test it out.