Editing genies through DBF Files

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Editing genies through DBF Files
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Commander olivier_vallee
34
Oncom
Commander Oncom
6
Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
2
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to AVEVA Plant SCADA Forum
Start a Topic
Solved
XavierVilabril
Crewman XavierVilabril
Crewman

Posted: ‎2025-09-08 05:12 AM

0 Likes
2
417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-08 05:12 AM

Editing genies through DBF Files

Hello,

 

I am in need of performing specific changes on a project with hundreds of thousands of tags and several hundred pages. I managed to mass-edit variables using an excel macro paired with the ProjectDBFTool. However,

 

I am facing issues regarding genie changes. I need to change genies to contemplate the changes I performed on the variables and change some genie types. I can find several DBF's pertaining to page layouts and such.

 

However, I cannot find the DBF page where genie instantiations are held. The closest thing i can find are CTG and CTF files, are these the only files holding this type of information? Is there no way to change file data to mass-update genies?

 

Thank you.

Labels
  • Labels:
  • Graphics Builder
  • Plant SCADA Studio
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
olivier_vallee
Commander olivier_vallee
Commander

Posted: ‎2025-09-08 05:02 PM

0 Likes
0
409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-08 05:02 PM

Hi @XavierVilabril 

The only way to mass-edit pages or their content is via the Graphics Builder Automation interface. See online help here for more details:

https://docs.aveva.com/bundle/plant-scada/page/1152714.html

Now, the CTG file is where all graphics object instance and page are stored. The CTM is the Genie Library and the CTL is the Page Template library. These are each proprietary files. The CTF is just a bitmap used for fast runtime display functionality.

It is only possible to edit the graphics files via the Graphics Builder application or the GB Automation interface. 

The Page DBF files (pg****.dbf) are basically output files by the graphics editor from the source data, contained in the CTG files. These DBF files are only used by the compiler to then create RDB files (used by runtime). Since the compiler was not designed to read the CTG file directly, it goes through this intermediate DBF file. This means that you can't edit the DBF files to make any changes (that are long lasting). Since the source of truth is the CTG which will overwrite any changes made to the DBF.

Hope this information helps you.

Kind regards

Olivier

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
olivier_vallee
Commander olivier_vallee
Commander

Posted: ‎2025-09-08 05:02 PM

0 Likes
0
410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-08 05:02 PM

Hi @XavierVilabril 

The only way to mass-edit pages or their content is via the Graphics Builder Automation interface. See online help here for more details:

https://docs.aveva.com/bundle/plant-scada/page/1152714.html

Now, the CTG file is where all graphics object instance and page are stored. The CTM is the Genie Library and the CTL is the Page Template library. These are each proprietary files. The CTF is just a bitmap used for fast runtime display functionality.

It is only possible to edit the graphics files via the Graphics Builder application or the GB Automation interface. 

The Page DBF files (pg****.dbf) are basically output files by the graphics editor from the source data, contained in the CTG files. These DBF files are only used by the compiler to then create RDB files (used by runtime). Since the compiler was not designed to read the CTG file directly, it goes through this intermediate DBF file. This means that you can't edit the DBF files to make any changes (that are long lasting). Since the source of truth is the CTG which will overwrite any changes made to the DBF.

Hope this information helps you.

Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

XavierVilabril
Crewman XavierVilabril
Crewman

Posted: ‎2025-09-09 02:00 AM

1 Like
0
387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-09 02:00 AM

Thank you Olivier, I will look into the automation interface!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore