A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-14 03:46 AM
Hi
I have just reinstalled a win 10 machine after a crash.
My Citect 2018 R2 application is up and running again, but all my Values are WAY off they bounch up and down all the time.
its normal undtil I edit the Citect.ini file with theese MODNET settings.
[modnet]
FloatMode = 1
LongDataType = 1
StringReverse = 1
Normal this work for me.. but not this time
Is there another place i can adjust these setting in 2018 R2 ?
Regards
Peter
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-14 03:58 AM
To fast
Problem is Solved..
I have 2 citect.ini files !!!
one in the Project folder and one in a Config folder..
and i only edit the one in the project folder which is NOT in use !!
Regards
Peter