Aveva Plant Scada 2023 R2 read tag with symbolic address from GE 90-30 PLC using GETCP driver

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Aveva Plant Scada 2023 R2 read tag with symbolic address from GE 90-30 PLC using GETCP driver
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Commander olivier_vallee
34
Oncom
Commander Oncom
6
Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
2
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to AVEVA Plant SCADA Forum
Start a Topic
Solved
job517
Crewman job517
Crewman

Posted: ‎2025-08-04 12:41 PM

0 Likes
3
599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-04 12:41 PM

Aveva Plant Scada 2023 R2 read tag with symbolic address from GE 90-30 PLC using GETCP driver

Hi everyone, I m working on a project that includes General electric plc and aveva plant scada . The versions are as follow:

Aveva Plant Scada 2023 R2 v8.50

General Electric PACSystems RX3i / CPU type IC695CPU310 / using Ethernet module IC695ETM001

Protocol is TCP using GETCP driver

I downloaded the GETCP driver since it was not included in the plant scada installation.

When I open the "Driver reference help" I can see the address format for reading various variable on the PLC(see attachedd image)

Since there is no mention of Symbolic addressing I doubt plant scada can read symbolic addresses from the GE plc. I have no means of testing this. In the meantime I just use the tagname /variable name  in the address colomn in plant scada . not sure if it will work.

 

Has anyone tried using symbolic address between Aveva plant scada and GE Fanuc PLC using the GETCP driver?

Thank you for your assistance 

Attachments
Labels
  • Labels:
  • Plant SCADA Studio
  • Tags:
  • driver
  • english
  • GETCPdriver
  • PlantSCADAdriver
  • SymbolicAddressing
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
olivier_vallee
Commander olivier_vallee
Commander

Posted: ‎2025-08-10 05:57 PM

1 Like
0
573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-10 05:57 PM

Hi @job517 

The GETCP driver does not support symbolic addressing.

As @sinced mentioned, the best approach would be to use a 3rd Party OPC Server (DA or UA) then use the Plant SCADA OPC (DA or UA) driver.

Kind regards

Olivier

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
sinced
Ensign sinced
Ensign

Posted: ‎2025-08-05 08:03 AM

1 Like
1
591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-05 08:03 AM

Use an OPC Server if you want to use symbolic addresses.

Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
Commander olivier_vallee
Commander

Posted: ‎2025-08-10 05:57 PM

1 Like
0
574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-10 05:57 PM

Hi @job517 

The GETCP driver does not support symbolic addressing.

As @sinced mentioned, the best approach would be to use a 3rd Party OPC Server (DA or UA) then use the Plant SCADA OPC (DA or UA) driver.

Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

job517
Crewman job517
Crewman

Posted: ‎2025-08-12 04:48 AM

In response to sinced
0 Likes
0
558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-12 04:48 AM

Thank You @sinced  I ended up with more than a 1000 errors when writing tag names under the address colomn .

Clearly the Driver does not support symbolic Addressing. OPC is the way to go

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore