Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:50 PM . Last Modified: 2024-03-21 01:34 AM
Hello All
I need to get a UPS for a system working on 230V using 5-15A
I would like to:
1. regulate the voltage during normal operation
2. have alternative power for 12 second during power fail- until emergency power generator kicks in. ( 1 min will be nice to have)
The catch:
System require more than 35 Amp during start up for ~5 second or so ( rough pump - E2M28 BOC EDWARDS)
Note that we are NOT going to turn the system ON while power in out.
So UPS system do not need to go that high while power in up or down.
We would like to have smaller inverter and battery thus cost with just a ~10 sec bypass while power is up for the start up
Normal consumption is in the range of 5-15 Amp as mentioned before (~7.5 -10A realistic) ) .
Looking forward to hear what solution you have for that case not just using a bigger UPS
Thx for all
OG
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:50 PM . Last Modified: 2024-03-21 01:34 AM
thank you for the reply
I guess I am missing using a step-up transformer
We are taking two 120 / 15A phases and creating single phase 208 which go into a step up transformer which is giving 220-240 on a good day.
There is also a slow blow fuse to overcome this 30A or so for short time.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:50 PM . Last Modified: 2024-03-21 01:34 AM
we have been talking amps and volt amps, do you have any wattage rating on this piece of equipment? this would be a more accurate measure of the power draw over volt amps so we can find out what would be best for you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:50 PM . Last Modified: 2024-03-21 01:34 AM
before even looking at UPS would appropriately suit this situation, i would think that if you are trying to handle an inrush of 35 amps on a 15 amp circuit, it would trip the upstream breaker. am i missing something?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:50 PM . Last Modified: 2024-03-21 01:34 AM
thank you for the reply
I guess I am missing using a step-up transformer
We are taking two 120 / 15A phases and creating single phase 208 which go into a step up transformer which is giving 220-240 on a good day.
There is also a slow blow fuse to overcome this 30A or so for short time.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.