Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

"Overloaded" and beeping with only 40 watts drawn (of the 390w UPS)

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • "Overloaded" and beeping with only 40 watts drawn (of the 390w UPS)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 08:18 AM . Last Modified: ‎2024-03-26 03:29 AM

0 Likes
1
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:18 AM . Last Modified: ‎2024-03-26 03:29 AM

"Overloaded" and beeping with only 40 watts drawn (of the 390w UPS)

Hi there,

 

I purchased a brand new APC 700VA 390 watt Back-Up's UPS for my small commsrack in my home office that consists of 3 devices:

  •  Fibre Network Termination Device (NTD)
  • Ubicquti Edge Router 4 (Router)
  • Juniper EX2200 PoE (Switch) - no PoE devices plugged in though.

I installed the Powerchute software to my computer and I monitored the load. With the UPS fully charged these three devices combined take 40 watts of power. I've run some tests and each test I pull the mains from it, the UPS goes into "overloaded" mode and has a constant beeping tone coming from it. So I did various troubleshooting and isolation tests, and found that the cause was the Juniper EX2200 PoE switch, the UPS also failed to work with a number of other PoE switches including Cisco and HP, I swap it out with an EX2200 non-PoE switch or Cisco 2960 non-PoE and the power stays on.

So as evident the PoE switch is at fault here - ok, fair enough.

Is there any explanation as to why the UPS can't handel switching over to the PoE switch even when there is no PoE devices running, and the total draw power from the UPS is <40 watts. I would understand if all 24 or 48 ports had active PoE devices on them, but a very bare setup, <40 watts it drops.

What VA UPS would be required to sustain the change over from Mains to UPS?, 1000?, 1500?.

 

Thanks in advanced.

Michael.

 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 390
  • 700va
  • overload
  • overloaded
  • watt
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 08:18 AM . Last Modified: ‎2024-03-26 03:29 AM

0 Likes
0
1123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:18 AM . Last Modified: ‎2024-03-26 03:29 AM

Bump. Anyone?.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 08:18 AM . Last Modified: ‎2024-03-26 03:29 AM

0 Likes
0
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:18 AM . Last Modified: ‎2024-03-26 03:29 AM

Bump. Anyone?.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore