Posted: 2021-06-28 04:31 AM . Last Modified: 2024-03-27 01:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:31 AM . Last Modified: 2024-03-27 01:40 AM
hi
in our EMI lab UPS power line switching noise @ 19.2 KHz is leaking up to 107 dBuV refer below graph, hence we are not able to conduct the CE measurement , We required the leakage of switching noise level 5dB below the pink line (Approx 85 to 90).pls suggest suitable model or aditional options to resolve my issue
regards
Raju
9880018403
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:31 AM . Last Modified: 2024-03-27 01:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:31 AM . Last Modified: 2024-03-27 01:40 AM
Hi,
Thank you for the revert. we are using SURT20KUXI. pls share how we need to connect the capacitor.its 3:3 configaration
best Regards
Raju kv
9880018403
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:31 AM . Last Modified: 2024-03-27 01:40 AM
I informally asked an EMI engineer about your question.
He told me that most of our UPSes are designed for data center environments and then meet class A rather than class B. The class A limits are higher.
Further, he thinks the noise is coming from the UPS' PFC or power supply. Since it's differential, you could add inductance to the line or a 10 uF line to line capacitor.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:31 AM . Last Modified: 2024-03-27 01:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:31 AM . Last Modified: 2024-03-27 01:40 AM
Hi,
Thank you for the revert. we are using SURT20KUXI. pls share how we need to connect the capacitor.its 3:3 configaration
best Regards
Raju kv
9880018403
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of