how to run self test, and a general problem with my ups

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • how to run self test, and a general problem with my ups
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:05 PM . Last Modified: ‎2024-03-26 01:37 AM

0 Likes
2
784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 PM . Last Modified: ‎2024-03-26 01:37 AM

how to run self test, and a general problem with my ups

Hi all,
This is a long post, sorry. Want to try and get all the relevant info out here the first time.

Background:
I have a Back UPS ES 750. Lately it has started switching back and forth from line to battery. It doesn't stay on battery long enough to start making alarm sounds or to signal a shutdown to the computer, but it will continue to switch back and forth until it's dead and the computer crashes. Actually the alarm did start sounding last night, but it was down to 3% battery power before that happened. Can't find a reason as far as other items on the same circuit, etc. Totally random when it happens too. Middle of the day, late at night, weekend, weekday, etc.

Self Test:
This happened one time before, it lasted for a few days, went away and everything was perfect until now. This was maybe a year ago. Tech support had me do something with the power button for a self test, count the beeps or something, I truly don't remember the details, just that we did it while I was on the phone. He told me the unit was broken. I called back a day later because I wasn't happy with that diagnosis and a different tech told me we did the test wrong (had power to the APC, or maybe didn't have power to the APC). Everything was okay then and started working just fine. I chalked it up to construction in the area screwing up the power quality. So I'd like to run this test again. Can anyone here tell me how to do that?

Other questions:
Any ideas what could cause this other than dirty power? I don't have access to any microsoft based products, so Powerchute is worthless for me. I'm going to have a friend of mine with windows adjust the sensitivity on the unit for me and give it back. Maybe that will help. I did notice that last night after I shut off the Mac, the unit immediately stopped switching back and forth from line to battery.

Is this normal for the unit to stop switching if it has no load?
Will overload conditions cause the unit to switch like that? The only thing plugged in that was on was the Mac. I'd like some reassurance that nothing is wrong with it, ie pulling too much current, that would cause the APC to oscillate.

Thanks!

Message was edited by: partsmutt

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:05 PM . Last Modified: ‎2024-03-26 01:37 AM

0 Likes
0
783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 PM . Last Modified: ‎2024-03-26 01:37 AM

Hi all,
This is a long post, sorry. Want to try and get all the relevant info out here the first time.

Background:
I have a Back UPS ES 750. Lately it has started switching back and forth from line to battery. It doesn't stay on battery long enough to start making alarm sounds or to signal a shutdown to the computer, but it will continue to switch back and forth until it's dead and the computer crashes. Actually the alarm did start sounding last night, but it was down to 3% battery power before that happened. Can't find a reason as far as other items on the same circuit, etc. Totally random when it happens too. Middle of the day, late at night, weekend, weekday, etc.

Self Test:
This happened one time before, it lasted for a few days, went away and everything was perfect until now. This was maybe a year ago. Tech support had me do something with the power button for a self test, count the beeps or something, I truly don't remember the details, just that we did it while I was on the phone. He told me the unit was broken. I called back a day later because I wasn't happy with that diagnosis and a different tech told me we did the test wrong (had power to the APC, or maybe didn't have power to the APC). Everything was okay then and started working just fine. I chalked it up to construction in the area screwing up the power quality. So I'd like to run this test again. Can anyone here tell me how to do that?

Other questions:
Any ideas what could cause this other than dirty power? I don't have access to any microsoft based products, so Powerchute is worthless for me. I'm going to have a friend of mine with windows adjust the sensitivity on the unit for me and give it back. Maybe that will help. I did notice that last night after I shut off the Mac, the unit immediately stopped switching back and forth from line to battery.

Is this normal for the unit to stop switching if it has no load?
Will overload conditions cause the unit to switch like that? The only thing plugged in that was on was the Mac. I'd like some reassurance that nothing is wrong with it, ie pulling too much current, that would cause the APC to oscillate.

Thanks!

Message was edited by: partsmutt

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:05 PM . Last Modified: ‎2024-03-26 01:37 AM

0 Likes
0
783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 PM . Last Modified: ‎2024-03-26 01:37 AM

Thanks EZ. So far it looks like the sensitivity adjustment has done the trick. In the 5 years since I switched to a Mac, this is the first time I've been required to go to a windows machine to get something done. I really wish APC would support us better.

Good thing this discussion forum is here.



Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:05 PM . Last Modified: ‎2024-03-26 01:37 AM

0 Likes
0
784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:05 PM . Last Modified: ‎2024-03-26 01:37 AM

Hi all,
This is a long post, sorry. Want to try and get all the relevant info out here the first time.

Background:
I have a Back UPS ES 750. Lately it has started switching back and forth from line to battery. It doesn't stay on battery long enough to start making alarm sounds or to signal a shutdown to the computer, but it will continue to switch back and forth until it's dead and the computer crashes. Actually the alarm did start sounding last night, but it was down to 3% battery power before that happened. Can't find a reason as far as other items on the same circuit, etc. Totally random when it happens too. Middle of the day, late at night, weekend, weekday, etc.

Self Test:
This happened one time before, it lasted for a few days, went away and everything was perfect until now. This was maybe a year ago. Tech support had me do something with the power button for a self test, count the beeps or something, I truly don't remember the details, just that we did it while I was on the phone. He told me the unit was broken. I called back a day later because I wasn't happy with that diagnosis and a different tech told me we did the test wrong (had power to the APC, or maybe didn't have power to the APC). Everything was okay then and started working just fine. I chalked it up to construction in the area screwing up the power quality. So I'd like to run this test again. Can anyone here tell me how to do that?

Other questions:
Any ideas what could cause this other than dirty power? I don't have access to any microsoft based products, so Powerchute is worthless for me. I'm going to have a friend of mine with windows adjust the sensitivity on the unit for me and give it back. Maybe that will help. I did notice that last night after I shut off the Mac, the unit immediately stopped switching back and forth from line to battery.

Is this normal for the unit to stop switching if it has no load?
Will overload conditions cause the unit to switch like that? The only thing plugged in that was on was the Mac. I'd like some reassurance that nothing is wrong with it, ie pulling too much current, that would cause the APC to oscillate.

Thanks!

Message was edited by: partsmutt

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore