Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

differences between es,cs,ls,rs

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • differences between es,cs,ls,rs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:15 AM

0 Likes
1
3886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:59 PM . Last Modified: ‎2024-03-21 03:15 AM

differences between es,cs,ls,rs

I have been trying to figure out the differences/advantages between the various families of UPS.
What advantages does the CS line have over the ES line ? LS over CS, RS over LS

The web pages dont seem to be much help here,
I am looking for technical data and features instead of uninformative quotes like
"best value" verses "High Performance"

In the past I have used RS for my PC and have been quite happy,
but now I am looking for UPS to protect against short blackouts
for things like TIVO, Cable Boxes, etc
I am hoping one of the "best value" lines will be enough, but I need some real data.
I can figure the watts, it is the other features I am struggling with.

thanks for your help

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:00 PM . Last Modified: ‎2024-03-21 03:15 AM

0 Likes
0
3886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:00 PM . Last Modified: ‎2024-03-21 03:15 AM

hi,

i will try to give you the quick version off the top of my head 🙂

•The ES line is geared towards home and home office applications. these only go up to 750VA and are a "brick style" meaning the outlets are on the top. Certain outlets are battery+surge protection, certain are always on and just surge protection only. They dont have as many LEDs on them to indicate status to you such as overload, on battery, etc but still give you audible alarms. their support through powerchute personal edition is there but for instance, you cant tell the UPS to run a self test from the software and you cant disable the self test function. these models do not have any automatic voltage regulation.

•The CS line is limited. They kind of look like the RS models but only go up to 500VA. These are a step up from the ES model and are kind of like the tower model versions of the ES line. They have more LED indicators on the front - Online, on battery, Replace battery, or overload. I dont believe these have automatic voltage regulation either. These are a "tower model" and still have battery+surge outlets and then just plain surge only outlets.

•The LS line is our "ergonomic" line. It has a different shape. It goes up to 700VA. This unit has automatic voltage regulation. I think it can only boost. It has 4 indicator lights on it like the CS line. The building wiring fault or site wiring fault light is located on the input plug. Other than that, I dont think any of these have coax protection on them. Only DSL, etc. I THINK you can tell the UPS to run a self test through software on these. I'd have to double check with one we have here.

•The RS line is the top of the line in the Back UPS family. They go up to 1500VA. They have automatic voltage regulation. They also have all types of data line protection depending on the model. They have the four indicator LEDs on the front. The BR1500 has the ability to add on an extended run battery pack. The 1500 I think you can also somehow put it in a rack if you lay it on its side. You can tell the UPS to run a self test through software on these.

On all of these you can manage them with powerchute personal edition to monitor line voltage, reasons it transferred to battery, etc or you can configure native power options on your operating system for graceful unattended shutdown of your computer (powerchute can also do this). All of them have user replacable batteries and have a three year warranty. they also all output a step approximated sine wave. i think it all depends on what you want for shape, style, data line protection, and wattage capability.

please let me know if you have more specific questions. I am not sure exactly what you are looking for and if i went through every single difference, i'd be typing for a day. hope this helps!

just a note, we have an AV line of products you can check out here: http://www.apc.com/products/category.cfm?id=15

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:00 PM . Last Modified: ‎2024-03-21 03:15 AM

0 Likes
0
3887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:00 PM . Last Modified: ‎2024-03-21 03:15 AM

hi,

i will try to give you the quick version off the top of my head 🙂

•The ES line is geared towards home and home office applications. these only go up to 750VA and are a "brick style" meaning the outlets are on the top. Certain outlets are battery+surge protection, certain are always on and just surge protection only. They dont have as many LEDs on them to indicate status to you such as overload, on battery, etc but still give you audible alarms. their support through powerchute personal edition is there but for instance, you cant tell the UPS to run a self test from the software and you cant disable the self test function. these models do not have any automatic voltage regulation.

•The CS line is limited. They kind of look like the RS models but only go up to 500VA. These are a step up from the ES model and are kind of like the tower model versions of the ES line. They have more LED indicators on the front - Online, on battery, Replace battery, or overload. I dont believe these have automatic voltage regulation either. These are a "tower model" and still have battery+surge outlets and then just plain surge only outlets.

•The LS line is our "ergonomic" line. It has a different shape. It goes up to 700VA. This unit has automatic voltage regulation. I think it can only boost. It has 4 indicator lights on it like the CS line. The building wiring fault or site wiring fault light is located on the input plug. Other than that, I dont think any of these have coax protection on them. Only DSL, etc. I THINK you can tell the UPS to run a self test through software on these. I'd have to double check with one we have here.

•The RS line is the top of the line in the Back UPS family. They go up to 1500VA. They have automatic voltage regulation. They also have all types of data line protection depending on the model. They have the four indicator LEDs on the front. The BR1500 has the ability to add on an extended run battery pack. The 1500 I think you can also somehow put it in a rack if you lay it on its side. You can tell the UPS to run a self test through software on these.

On all of these you can manage them with powerchute personal edition to monitor line voltage, reasons it transferred to battery, etc or you can configure native power options on your operating system for graceful unattended shutdown of your computer (powerchute can also do this). All of them have user replacable batteries and have a three year warranty. they also all output a step approximated sine wave. i think it all depends on what you want for shape, style, data line protection, and wattage capability.

please let me know if you have more specific questions. I am not sure exactly what you are looking for and if i went through every single difference, i'd be typing for a day. hope this helps!

just a note, we have an AV line of products you can check out here: http://www.apc.com/products/category.cfm?id=15

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore