bx1000g gives F02 error
  • bx1000g gives F02 error
2151
120
Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-27 01:34 AM
5544
I purchased a used XS1000 (BX1000g) that when you first plug it in gives a F02 error.  Turned it off via the power button and then back on.  Battery indicator just flashes and no power through any of the outlets.  Didn't test this with a lamp but did test with cell phone and power adaptor.  Is this a battery issue or a defective unit?
Any help would be greatly appreciated.
  • bx1000g
  • f02
  • xs
  • xs1000
F2 error equals On-battery output short. The errors are listed in the User's Guide on page 5. The solution listed is
Turn the Back-UPS off. Disconnect non-essential equipment from the Battery Backup outlets and the turn Back-UPS on. If that does not resolve the issue try a reset.
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket.
3: Disconnect the UPS' internal battery.
4: Push and hold the "On" button on the UPS for 5 seconds
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.
Have you contacted APC  about this?
I have a feeling they might want to see that one.    I'm fairly sure they'd cover the costs in this case.
I've never heard of one literally burning.
Posted: ‎2021-06-28 04:43 AM . Last Modified: ‎2024-03-27 01:34 AM
Sorry for the inconvenience. You should contact local support immediately for assistance. http://www.apc.com/fi/en/support/contact-us/index.jsp
Replies 4
7: Turn UPS on.
Our UPS showed the error code F02 for a very short while before it disappeared, and within five minutes the fire started. Not fun.