Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84595members
353862posts

blinking battery light on back ups 1500

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
will2013_apc
Cadet
0 Likes
1
133

blinking battery light on back ups 1500

This was originally posted on APC forums on 11/26/2013


inherited a 2 yo lightly used APC back ups 1500, battery light blinking, not used in a year, displays no error code, safe to assume it just needs a long charge up?  Manual is a bit vague but assuming it has just been unplugged too long and trickle drained? 


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
133

Re: blinking battery light on back ups 1500

This reply was originally posted by Angela on APC forums on 11/27/2013


Yes, you can try letting it charge up. Anytime a UPS is stored, you should disconnect the battery and periodically charge it around every six months.

I'll assume this is the replace battery LED flashing (versus on battery)? This means the UPS thinks the battery is disconnected which if it is not charged and has a low voltage, it could appear "missing" or disconnected.

So, it is worth letting it try to charge in the UPS for a day or so but if it doesn't go away, the battery may be damaged and unable to hold a charge. You could also measure the DC voltage on the battery if you have a voltmeter.

Depending how that turns out, rarely this can be a fault where the UPS mistakenly reports that but I doubt it for how the battery and UPS hasn't been in use for a while. Once you let it charge, you could test the unit's operation by removing AC power/pulling the plug to see if the UPS transfers to battery and supports the load or if it cannot and possibly turns itself off too.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
134

Re: blinking battery light on back ups 1500

This reply was originally posted by Angela on APC forums on 11/27/2013


Yes, you can try letting it charge up. Anytime a UPS is stored, you should disconnect the battery and periodically charge it around every six months.

I'll assume this is the replace battery LED flashing (versus on battery)? This means the UPS thinks the battery is disconnected which if it is not charged and has a low voltage, it could appear "missing" or disconnected.

So, it is worth letting it try to charge in the UPS for a day or so but if it doesn't go away, the battery may be damaged and unable to hold a charge. You could also measure the DC voltage on the battery if you have a voltmeter.

Depending how that turns out, rarely this can be a fault where the UPS mistakenly reports that but I doubt it for how the battery and UPS hasn't been in use for a while. Once you let it charge, you could test the unit's operation by removing AC power/pulling the plug to see if the UPS transfers to battery and supports the load or if it cannot and possibly turns itself off too.