XS 1300 Battery Replacement Questions?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • XS 1300 Battery Replacement Questions?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
122
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

0 Likes
2
2149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

XS 1300 Battery Replacement Questions?

So the replace battery light (the battery with an X through it) lit up today on my XS 1300. I think I bought it around 3 or 4 years ago so I don't believe it's still under warranty. I think I'm gonna replace the batteries, but I wanted to ask a few questions here before spend the money.
-How reliable is the replace battery light? Since new batteries are most likely not returnable, I'd like to be sure they are actually bad before I buy them.
-Other than the battery backup, the UPS seems to work fine. Is it safe to continue to use the UPS with the battery light on or with the battery pack not installed?
-Any suggestions on a good place to buy replacement batteries? The APC replacement is a bit costly for a couple of standard 12v 9Ah lead acid batteries, so I'd like to explore other options.
-Can I upgrade the batteries to 12Ah or should I stick with what it came with?
Any other advice from others who have swapped out the battery packs on their XS 1300 is welcome.

Thank You,
JCuervo

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

0 Likes
0
2149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

The RBL (replace battery light) can either be off, flashing or solid. Do you recall if it was flashing or solid? If the RBL was flashing, it means that the UPS has a disconnected battery condition. If it is a solid RBL it means that there is a bad battery on the UPS. To check if it is indeed a bad battery we advise our customer to perform a self-test. Self test can be done by pressing and holding the On/Test button while the unit is online. Once you see the Online LED is flashing the button needs to be released. If the RBL would still come on solid it just tells you again that a battery is indeed bad.

With the RBL on, you can still use the surge only outlets of the UPS. This would still be on and would give you the surge protection that you need. With regards to upgrading/changing the battery into a different specifications I would say for you to stay on the original rating of the battery. Our UPS is designed to use that specific battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

0 Likes
0
2149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

I'm pretty sure the RBL was solid, it also started making a chirping sound. I left it unplugged overnight and when I plugged it in today, the RBL wasn't on but the battery was dead. I ran the self-test and it didn't report anything wrong, so I let it sit and charge for about 8 hours. When I turned the unit back on, the battery showed a charge, but when I unplugged it and let it go into battery mode, the charge dropped off fast. If I plug something into one of the outlets the unit shuts down immediately, even if the battery meter shows half full. I pulled out the batteries and did a load test with my multimeter and I think only one is bad. Is it ok to replace just one of the batteries in the pack or do I need to replace them as a pair? The only other concern I have is that, around the time the RBL lit up, I noticed a little bit of burnt electronics smell blowing out the back vent when the fan came on. I smelled it again when I was testing the UPS in battery mode, but it seemed to go away after a little while. The batteries haven't been cycled in a while so I wonder if it could just be some dust burning off due to the heat emitted during charging/discharging. Thanks for your help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

0 Likes
0
2150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

The RBL (replace battery light) can either be off, flashing or solid. Do you recall if it was flashing or solid? If the RBL was flashing, it means that the UPS has a disconnected battery condition. If it is a solid RBL it means that there is a bad battery on the UPS. To check if it is indeed a bad battery we advise our customer to perform a self-test. Self test can be done by pressing and holding the On/Test button while the unit is online. Once you see the Online LED is flashing the button needs to be released. If the RBL would still come on solid it just tells you again that a battery is indeed bad.

With the RBL on, you can still use the surge only outlets of the UPS. This would still be on and would give you the surge protection that you need. With regards to upgrading/changing the battery into a different specifications I would say for you to stay on the original rating of the battery. Our UPS is designed to use that specific battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

0 Likes
0
2150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-21 05:26 AM

I'm pretty sure the RBL was solid, it also started making a chirping sound. I left it unplugged overnight and when I plugged it in today, the RBL wasn't on but the battery was dead. I ran the self-test and it didn't report anything wrong, so I let it sit and charge for about 8 hours. When I turned the unit back on, the battery showed a charge, but when I unplugged it and let it go into battery mode, the charge dropped off fast. If I plug something into one of the outlets the unit shuts down immediately, even if the battery meter shows half full. I pulled out the batteries and did a load test with my multimeter and I think only one is bad. Is it ok to replace just one of the batteries in the pack or do I need to replace them as a pair? The only other concern I have is that, around the time the RBL lit up, I noticed a little bit of burnt electronics smell blowing out the back vent when the fan came on. I smelled it again when I was testing the UPS in battery mode, but it seemed to go away after a little while. The batteries haven't been cycled in a while so I wonder if it could just be some dust burning off due to the heat emitted during charging/discharging. Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore