Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Using ES 550VA on an appliance

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Using ES 550VA on an appliance
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:13 AM . Last Modified: ‎2024-03-22 02:44 AM

0 Likes
3
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:13 AM . Last Modified: ‎2024-03-22 02:44 AM

Using ES 550VA on an appliance

I have a pellet burning stove that if running and power is lost the room fills with smoke. I need about 5 minutes to switch the unit to off the exhaust the stove. During this exhaust it draws 150 watts so the 550VA should be fine. My question is the problem I've read about with the continuous alarm that sounds, will I be able to turn this off? Does this alarm go off whenever power is lost? There's a good chance power can be lost when the stove is not even running.
Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 02:13 AM . Last Modified: ‎2024-03-22 02:44 AM

0 Likes
0
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:13 AM . Last Modified: ‎2024-03-22 02:44 AM

Bob,

The Back UPS emits 4 beeps every 30 seconds when on Battery or during power failure. If you are referring to the Overload Continuous beep, then it can not be disabled or turned off.

FYI..APC K-base ID: 1356:

APC's Back-UPS line is designed for use with Computer-type loads only. They are not designed to be used with motor loads such as fish filters, air conditioning units, space heaters, vacuum cleaners or any other machinery.

One potential issue is the inrush current draw for a motor. It can easily overload a Back-Ups UPS model. Secondly, these models of UPSs output a Stepped-Approximated sine wave when on battery. This waveshape, while ideal for computer-type equipment, is not particularly compatible with most motor loads or other machinery. The result may be that motors run very slowly, erratically, or not at all when the UPS is on battery.

To protect this type of equipment, APC recommends first determining the appropriate size UPS for the motor load in question. Ensure that the Volt Amp rating of the UPS is sufficient to handle the start-up inrush current draw of the motor. Secondly, select a UPS which outputs a Pure Sine Wave when on battery, such as a Smart-UPS (minimum of a SUA700), Matrix-UPS, or Symmetra Power Array.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 02:13 AM . Last Modified: ‎2024-03-22 02:44 AM

0 Likes
0
1197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:13 AM . Last Modified: ‎2024-03-22 02:44 AM

Bob,

The Back UPS emits 4 beeps every 30 seconds when on Battery or during power failure. If you are referring to the Overload Continuous beep, then it can not be disabled or turned off.

FYI..APC K-base ID: 1356:

APC's Back-UPS line is designed for use with Computer-type loads only. They are not designed to be used with motor loads such as fish filters, air conditioning units, space heaters, vacuum cleaners or any other machinery.

One potential issue is the inrush current draw for a motor. It can easily overload a Back-Ups UPS model. Secondly, these models of UPSs output a Stepped-Approximated sine wave when on battery. This waveshape, while ideal for computer-type equipment, is not particularly compatible with most motor loads or other machinery. The result may be that motors run very slowly, erratically, or not at all when the UPS is on battery.

To protect this type of equipment, APC recommends first determining the appropriate size UPS for the motor load in question. Ensure that the Volt Amp rating of the UPS is sufficient to handle the start-up inrush current draw of the motor. Secondly, select a UPS which outputs a Pure Sine Wave when on battery, such as a Smart-UPS (minimum of a SUA700), Matrix-UPS, or Symmetra Power Array.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:13 AM . Last Modified: ‎2024-03-22 02:44 AM

0 Likes
0
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:13 AM . Last Modified: ‎2024-03-22 02:44 AM

Thanks very much for the info. To establish requirements I plugged the stove into a Kill-a-watt and monitored throughout all phases of operation and the watt usage ranged from 106 to 168.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 02:14 AM . Last Modified: ‎2024-03-22 02:44 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:14 AM . Last Modified: ‎2024-03-22 02:44 AM

If it can work off stepped approximation to a sine wave, then you can connect it to the Back UPS ES 550. Click here to view the BE550G UPS Runtime at different load levels.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore