UTS6H and breaker box leg feed questions

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS6H and breaker box leg feed questions
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:05 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
2
710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:05 PM . Last Modified: ‎2024-03-20 12:54 AM

UTS6H and breaker box leg feed questions

I was curious on the designed behavior with the UTS6H.  I understand the 110v/120v of the UTS6H vs 220v/240v nature of the UTS6(BI) and UTS10(BI) for the generator feed. I am considering the UTS6H with a Honda EU2000i but wanted to verify a few things.

With load balancing and wiring a 240v utility fed house at the breaker box without a transfer switch, the phase difference is how you end up with the 240v from the dual 120v utility feeds.  If you have the UTS6H and you pick (for argument sake) two circuits on the left half and four on the right half of the house breaker box, I do not believe you need to load balance the two halves as the UTS6H is only 120V driven from the generator.  Is wattage capacity your only/main concern at that point regarding proper setup? 

Are there issues with having circuits on different phases of the house feed and switching over to the single phase generator feed and back again or is there enough down time between sources that everything is fine?  Or, is there enough tolerance in household electronics to not care if the UTS causes the feed(s) to be out of sync for one half cycle if the source toggle is almost instantaneous?

Also is there a risk of what I would inappropriately call phase-lock between the left half and right half or does the UTS6H isolate the halves of your breaker box when running on utility power and merge them (the six circuits you wired into the UTS6h) when running on 120v generator?

One more question for tonight, should you set the maximum wattage for the generator in the UTS6H to the 2000 watt peak the EU2000i can handle for up to 30 minutes, set it down to 1600 watts that it can do continuous, or somewhere in the middle?

I imagine this is all me being overly cautious and it is perfectly safe to use the UTS6H on both halves of a two phase residential breaker box, but I wanted to verify phase-lock and circuit count wise being unbalanced were not issues.

Thank you

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • uts6h
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:05 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
0
710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:05 PM . Last Modified: ‎2024-03-20 12:54 AM

Hi squeegee,

When the UTS6H senses a loss in utility power, it will disconnect itself from the Main Distribution panel by closing a single relay for each circuit. The panel will remain inoperable for a minimum of 5 seconds, to ensure these relays latch open properly. This is referred to as CPLD or Circuit Protection Load Disconnect. By opening these relays, the UTS6H is capable of isolating itself from the Mains, as to not back-feed onto the utility source. Once isolated, the UTS6H is now capable of passing power directly from the attached generator to the desired loads without issue. Although the generator is sized for a maximum of 2000w peak, it may be best to reference the 1600-1800w as the generators maximum and allow the UTS panel to disconnect loads as it deems necessary through Adaptive Load Management. An option however which is strongly recommended, would be to add an additional UPS to the UPS inlet. This will provide you the additional watt capacity of the UPS during extended outages, in addition to your single phase generator.

I hope this helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:05 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
0
711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:05 PM . Last Modified: ‎2024-03-20 12:54 AM

Hi squeegee,

When the UTS6H senses a loss in utility power, it will disconnect itself from the Main Distribution panel by closing a single relay for each circuit. The panel will remain inoperable for a minimum of 5 seconds, to ensure these relays latch open properly. This is referred to as CPLD or Circuit Protection Load Disconnect. By opening these relays, the UTS6H is capable of isolating itself from the Mains, as to not back-feed onto the utility source. Once isolated, the UTS6H is now capable of passing power directly from the attached generator to the desired loads without issue. Although the generator is sized for a maximum of 2000w peak, it may be best to reference the 1600-1800w as the generators maximum and allow the UTS panel to disconnect loads as it deems necessary through Adaptive Load Management. An option however which is strongly recommended, would be to add an additional UPS to the UPS inlet. This will provide you the additional watt capacity of the UPS during extended outages, in addition to your single phase generator.

I hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

0 Likes
0
710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:06 PM . Last Modified: ‎2024-03-20 12:54 AM

Thank you SecretSquirrel.

From the sounds of it, consider my home's breaker box as it is, and consider the UTS6H as it's own complete setup.  The isolation of the circuits with the relays take the balance out of concern with the UTS6H being single sided with 120v.

We shall see how fast the wife lets me invest in this, she has a hard time believing we have any need due to only loosing power once in over ten years for more than five minutes, and only two blips for a few seconds.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of