Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82470members
350042posts

UTS6H Hardwire Kit question

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
FKFW_apc
Cadet
0 Likes
1
124

UTS6H Hardwire Kit question

This was originally posted on APC forums on 11/8/2019


I recently installed a UTS6H in my house. I discovered that I cannot run a generator feed into the UPS inlet and still have 6 circuits available. I contacted tech support and they told me to get the Hardwire Kit. 

Done. Got the Hardwire Kit. The kit's instructions show the removal of a circular inlet plug on the front of the unit in order to facilitate the Hardwire KIt, but my UTS6H has no circular plug on the front.

Any suggestions?

Thanks.

Attachments

Accepted Solutions
wayne_i_apc
Lieutenant
Lieutenant
0 Likes
0
124

Re: UTS6H Hardwire Kit question

This was originally posted on APC forums on 1/10/2020


The UPS inlet was NOT intended to be used as the generator input to the UTS. Because the UPS inlet is only rated at 15A, it would not provide enough power to distribute to all 6 UTS load circuits and as you have learned, circuit 1 does not receive power from the UPS inlet. Older versions of the UTS had a front panel generator plug which would be disconnected and removed when the hardwire kit was installed. If there is an opening on your front panel where the circular generator plug was formerly installed, install the "close-off plate" included with the kit, and follow the remaining instructions. When a generator is connected to the UTS using the hardwire kit up to 30A at 120 volts can be distributed to all 6 circuits in the UTS6H.

I hope this helps!

See Answer In Context

1 Reply 1
wayne_i_apc
Lieutenant
Lieutenant
0 Likes
0
125

Re: UTS6H Hardwire Kit question

This was originally posted on APC forums on 1/10/2020


The UPS inlet was NOT intended to be used as the generator input to the UTS. Because the UPS inlet is only rated at 15A, it would not provide enough power to distribute to all 6 UTS load circuits and as you have learned, circuit 1 does not receive power from the UPS inlet. Older versions of the UTS had a front panel generator plug which would be disconnected and removed when the hardwire kit was installed. If there is an opening on your front panel where the circular generator plug was formerly installed, install the "close-off plate" included with the kit, and follow the remaining instructions. When a generator is connected to the UTS using the hardwire kit up to 30A at 120 volts can be distributed to all 6 circuits in the UTS6H.

I hope this helps!