UTS6H Fuse Question

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UTS6H Fuse Question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
9
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

UTS6H Fuse Question

I have an UTS6H installed in my home.  My question is regarding the fuses used in the UTS.  Twice I've had to replace a fuse on a circuit, once because of a frayed vacuum cleaner cord and the other time after a light bulb burnt out.  Both times the fuse inside the UTS blew before the circuit breaker in my main panel tripped.  This is a huge inconvenience having to remove the UTS cover to service the fuse.  Not to mention these fuses are very expensive $15+ each??

My first question is why are these fuses in series while on Utility power?  I'm assuming they are present to protect the circuit while on generator power.

2. Why were fuses chosen and not resettable circuit breakers for this design?

3. Is there an easy way to convert these fuses to circuit breakers?

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

You are not alone with the night light's blowing a fuse in the UTS-6.

Happened to us last night - with the little extra twist of "Someone" just telling me that the lights in 2 bedrooms "stopped working"..... after about an hour of pulling the main breaker panel, pulling the cover on the UTS-6 and generally fooling around, it emerged that the "stopped working" was conincident with her night light making a flash and a noise..... -)

Must be something with those night light bulbs.

I note that all the fuses on my UTS-6 are fast-blow.   Do they have to be fast-blow?   Or will slow-blow work?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

I have an UTS6H installed in my home.  My question is regarding the fuses used in the UTS.  Twice I've had to replace a fuse on a circuit, once because of a frayed vacuum cleaner cord and the other time after a light bulb burnt out.  Both times the fuse inside the UTS blew before the circuit breaker in my main panel tripped.  This is a huge inconvenience having to remove the UTS cover to service the fuse.  Not to mention these fuses are very expensive $15+ each??

My first question is why are these fuses in series while on Utility power?  I'm assuming they are present to protect the circuit while on generator power.

2. Why were fuses chosen and not resettable circuit breakers for this design?

3. Is there an easy way to convert these fuses to circuit breakers?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

Hi erikd,

The UTS panel itself was designed to be placed in series between the Service panel and the Load for ease of use/installation, as well as additional functional benefits found in the UTS, i.e. Security Mode, Electrical Phase Status, etc.

Fuses were also chosen for specific reasons. Fuses are known to have a much more exact tripping point and faster response time than that of the typical circuit breaker. In addition, circuit breakers are designed to be tripped no more than 2-3 times as a result of a fault interruption, before requiring replacement. While the UTS fuses are easily replaceable in the field, miniature circuit breakers would require hard wiring to the UTS panel and involve extensive manipulation of the panel to replace these breakers. The UTS is considered a self contained electronic device, therefore the replaceable circuit breakers used in electrical service panels could not be used.

Although there is no way to convert the unit to circuit breakers, we have included a series of Male to Male fast-tons which would allow for by-pass of the fuse function if a fuse were to blow and no replacement fuse was available. This would enable the enduser/installer to reapply power to the circuit until a fuse could be acquired.

FYI; the Male to Male fast-tons are for use as a temporary repair and are not intended for continued use in place of the fuse.

SecretSquirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

Thanks for the reply.

I think that's my point.  Fuses are known to have a much more exact tripping point.  They will open before a circuit breaker will trip in many cases.  This effectively reverts my 6 circuits back to the 1940's, fumbling around in the dark trying to replace a fuse that has blow.  Which was the case just this past weekend when a night light bulb (believe it or not) that had burnt out rather violently and took out a fuse in the UTS.  Here's pic of the bulb.  You can see one electrode had actually melted.

1420_bulb.JPG

If code will not allow the use of electrical service panel breakers in the UTS then I would suggest changing the design so that the fuse is not in the circuit while on utility power.  The fuse is only needed while on generator or UPS power.  This would eliminate these nuisance fuse replacements 99% of time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

Is this also the case in "Bypass" mode?  Are the fuses in line with the load then?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

Yes, I believe so.  The fuses are always in line.  That would have been convenient option to re-energize a circuit with a blown fuse, to simply place that circuit in by-pass.  But based on the current design that would have required another bank of relays.  I believe By-Pass mode simply disables all UTS functions for that circuit but doesn't actually "by-pass" the UTS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

The Ferraz Shawmut fuses are $7.88 each at Zoro Tools, not cheap but better than list price. I keep several spare 15's and 20's just in case.

However, I have had my UTS10BI for over a year and haven't blown a fuse yet. When my wife uses her hair dryer on full blast, that circuit occasionally overloads. It always trips the overcurrent sensor in the UTS first, which shuts down the circuit. All I have to do is follow the instructions on the UTS display (basically just press any button on the UTS) to reset it, and it comes right back on. I have even trained my wife to do this in case I'm not there. I have also recommended that she not use the "high heat" setting on her hair dryer 😉

This is a 15 amp circuit, on a 15 amp breaker, set to a circuit amp rating of 15 amps in the UTS setup and with a 15 amp fuse in the UTS. And the UTS overcurrent sensor is always (at least so far) the first to trip, which is obviously better than blowing the fuse. Perhaps your overloads (i.e. blown light bulb) have been a little more "violent" than mine and that triggers the fuse first. In any event, you may want to double-check your UTS setup to make sure the circuit amp rating matches the UTS fuse as well as the circuit breaker.


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:25 PM . Last Modified: ‎2024-03-20 12:36 AM

You are not alone with the night light's blowing a fuse in the UTS-6.

Happened to us last night - with the little extra twist of "Someone" just telling me that the lights in 2 bedrooms "stopped working"..... after about an hour of pulling the main breaker panel, pulling the cover on the UTS-6 and generally fooling around, it emerged that the "stopped working" was conincident with her night light making a flash and a noise..... -)

Must be something with those night light bulbs.

I note that all the fuses on my UTS-6 are fast-blow.   Do they have to be fast-blow?   Or will slow-blow work?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:36 AM

I suspect the built-in over current sense protection is not designed for arc fault detection.  That too would also be an improvement in the design.  The relatively slow heating of an over current fault is quite different from that of a short circuit arc in terms of over current protection.  Don't get me wrong.  I really like this transfer switch idea and it worked beautifully during our last multi-day outage event but I'm just not thrilled about this fuse design.  I'll probably just change my two general lighting circuits to the slow blow ATDR series fuse and hope that time delay will absorb a light bulb burning out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:36 AM

0 Likes
0
1413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:26 PM . Last Modified: ‎2024-03-20 12:36 AM

That's amusing!  I can't believe someone else experienced this same situation!  Thanks for sharing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now